My furnace stopped working. I tried turning the power off

Customer Question

My furnace stopped working. I tried turning the power off and then right on again; the fan started blowing but the air is cold. Would it help to leave the power off for longer and then turn it back on? Is there anything else I can try?
Thank you!
Ailsa Nielsen
Submitted: 3 years ago.
Category: HVAC
Expert:  Matthew replied 3 years ago.

Matthew :

Hello, My name is XXXXX XXXXX I will do my best to help you today.

Matthew :

When power is turned off to a bryant furnace then right back on it will bring on the circulating blower for 90 secs and then the blower should cut off and the inducer motor should come on if there is a call for heat. This is the small motor hooked to the exhaust. If the circulating blower continues to run after the 90 secs none stop then the furnace has a tripped limit. On the furnace control board located behind the bottom door of the furnace there will be a small LED light blinking a fault code if this is the case. Let me know if the inducer ever starts up and if the LED ever gives you a fault code blink.

Customer :

Thank you. I am not sure how I would know if the inducer motor comes on. There is no heat.

Matthew :

With the thermostat calling for heat you would have to go down to the furnace and take the top door off. Then right next to the furnace there should be a little toggle switch cut off that turns high voltage power off to the furnace. Turn this switch off then back on and stand next to the furnace and observe what it does. You will know if the inducer is running with the top door off you can see the little wheel spinning.

Matthew :

Like I said before the blower will run for 90 secs and then should turn off and the inducer should start up and the ignition should take place. Just observe for 3-5 mins and let me know what the furnace is or isn't doing.

Customer :

Is the top door the one that is screwed on or the back side door with all the warnings about electric current?

Matthew :

don't know what the back side door is you are talking about. I think on a bryant the door is held in by a little nob in the middle maybe? follow the exhaust vent into the furnace and it will lead you to the inducer. Take the door off directly in front of the inducer. The gas pipe will lead in to this same area as well. The door should be louvered.

Customer :

We have opened the side door to the furnace - there is an off and on switch inside this door; I turned this off and then on (although I believe that this was the gas switch not the electricity). There is a little wheel but it is not spinning; also the furnace is rather loud when the fan is blowing.

Matthew :

the on off switch is on the gas valve. There should be a switch that looks like a light switch on the wall somewhere near the furnace. Need to turn this switch off and on to reset the furnace and see what it does.

Matthew :

found the 80T, it has one big door that exposes all the parts inside correct?

Matthew :

Full Size Image

Matthew :

Inside there should be a model number I need that number to pull up the specs on the unit and I can be much more specific with my directions.

Customer :

Yes, that is the door that we opened - I have turned the switch on and off a number of times; the only thing that happens is that the blower goes on and nothing else. Here is the model number: 312AAV042090

Matthew :

Do you see a blinking LED on the furnace control board?

Customer :

There is a blinking yellow light - I don't know what the LED or the furnace control board is

Matthew :

Full Size Image

Matthew :

The only things that would make the furnace blower run non stop when in heat mode is a tripped limit or a malfunctioning control board. There should be roll out limits that you can manually reset. These are located around the burners compartment. I'll send a picture. Just press the little button in the center down and see if the furnace tries to ignite then.

Matthew :

Full Size Image

Matthew :

This furnace omits it's fault codes with a 2 digit number. The led will blink a number of times slowly with drawn out flashes then it will blink of a number of times with fast brief flashes. This gives you a 2 digit number. 2 slow flashes then 3 fast flashes = fault code 23.

Customer :

The furnace blower is not running nonstop

Customer :

Is the burner's compartment behind the door that we removed?

Matthew :

yes. follow the pipe leaving the gas valve down to the burners. These burners are encased with metal around all sides and on this metal there should be these little limits with reset buttons I sent you a picture of.

Matthew :

So the furnace blower does stop eventually when power is reset but the inducer draft motor never kicks in?

Customer :

Yes, the blower does stop eventually. I'm inside the side door following the gas pipe and only locating one thing covered on all sides by metal - I cannot find the switch anywhere on this. There are small pipe-like things covered that lead into the furnace, but I am not finding the switch on these either.

Matthew :

Having a hard time figuring out what you are talking about sorry. Do you see the furnace control board with the blinking light? It may be through a little glass peep hole behind a panel covering the bottom of the furnace with the big door off.

Customer :

Yes, I see the blinking light behind the liggle glass peep hole. What information did you need from that? Also, I thought you wanted me to press some limit buttons that may ignite the furnace and I am having trouble locating these.

Customer :

The light is blinking three long lights and then three shorter lights - is that a 32?

Matthew :

33

Matthew :

is it 3 and 3 or 3 and 2?

Matthew :

we are getting somewhere now hang with me. If you can get me the correct blink code it will make life much easier

Customer :

It's three short lights and then two longer lights

Matthew :

perfect. okay this is your pressure switch. I need you to find the pressure switch with the yellow and orange wire hooked to it. I'll send a picture of what a pressure switch looks like. Your furnace has two. Find the one with the yellow and orange wires hooked to it. With the furnace still on and calling for heat pull one of these two wires off and tell me if the inducer draft motor starts up when you do.

Matthew :

Full Size Image

Matthew :

It has the yellow and orange wire hooked to it and also a rubber hose attached to it.

Customer :

I pulled the orange wire off and nothing happened.

Matthew :

okay. You have either a bad inducer draft motor or you have a bad control board. You need a volt meter in order to test for 120v going to the inducer. If there is 120v and the inducer isn't running then you need a new inducer draft motor. If there isn't 120v then you need a new control board.

Customer :

Thanks Matthew. Looks like we will need to have somebody come to the house and take care of the repairs

Matthew :

sorry it wasn't something miner. The board or the inducer motor are not the cheapest of parts. If your furnace is under 5 years old these parts are under warranty though.

JustAnswer in the News:

 
 
 
Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.
 
 
 

What Customers are Saying:

 
 
 
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
< Last | Next >
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
  • Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help. Mary C. Freshfield, Liverpool, UK
  • This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!! Alex Los Angeles, CA
  • Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult. GP Hesperia, CA
  • I couldn't be more satisfied! This is the site I will always come to when I need a second opinion. Justin Kernersville, NC
  • Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around. Esther Woodstock, NY
  • Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know. Robin Elkton, Maryland
 
 
 

Meet The Experts:

 
 
 
  • gotoman for ac

    HVAC Technician

    Satisfied Customers:

    4657
    51 years of experience install design and repair of all makes and models of AC
< Last | Next >
  • http://ww2.justanswer.com/uploads/SE/ServiceTechRus/2012-6-7_2119_056.64x64.JPG gotoman for ac's Avatar

    gotoman for ac

    HVAC Technician

    Satisfied Customers:

    4657
    51 years of experience install design and repair of all makes and models of AC
  • http://ww2.justanswer.com/uploads/AL/alumalite/2012-5-10_234018_shutterstock506249951forJA500.64x64.jpg Phil's Avatar

    Phil

    Mechanical Engineer

    Satisfied Customers:

    3888
    Retired HVAC/ Electrical & Boiler contractor. Industrial
  • http://ww2.justanswer.com/uploads/skibum0101/2008-12-16_015819_just_answer.jpg Rick Mather's Avatar

    Rick Mather

    HVAC Technician

    Satisfied Customers:

    3132
    35 years experience, HVAC
  • http://ww2.justanswer.com/uploads/RY/Rygis20/2011-5-7_3143_DSC5324.64x64.JPG Matthew's Avatar

    Matthew

    HVAC Technician

    Satisfied Customers:

    1994
    14 years experience in the HVAC field of service, installation, Manual J & D calculations
  • http://ww2.justanswer.com/uploads/KE/kentguidry/2011-9-26_214316_0059.64x64.jpg Kenton Guidry's Avatar

    Kenton Guidry

    HVAC Technician

    Satisfied Customers:

    962
    12 years install/service experience.
  • http://ww2.justanswer.com/uploads/solarman1947/2009-12-13_223915_phpkKBcXq_c2PM.jpg Rick Ridley's Avatar

    Rick Ridley

    UK Heating Engineer

    Satisfied Customers:

    871
    Retired But have had 30 years on the tools, Ex CORGI
  • http://ww2.justanswer.com/uploads/Ironheadfan/2009-12-18_222416_pump_005.jpg Tom's Avatar

    Tom

    HVAC Technician

    Satisfied Customers:

    770
    16+yrs HVAC/R service. Residential Commerical Industrial