I have a Reznor V3 T Core2 mdl no UDAP45 garage heater that

 
Tom's Avatar
  • Answered by:Tom
  • HVAC Technician
  • Positive Feedback: 99.8 %
  • Accepted Answers: 763
Verified Expert
in HVAC

Recent Feedback

Positive
Gave lots of insight on how to best solve my problem.
Positive
This guy was awesome! Super helpful and went really deep to explain the problem...
Positive
Very helpful! Walked me through troubleshooting my AC unit and isolating bad...
Positive
Tom was great!!! Could not have asked for a better tech
Positive
Took time and answered questions
Positive
Tom was absolutely amazing! Right answer fixed the problem & saved me a service...
Positive
Very helpfull. May possibly save me expensive repair bill.
Positive
Thanks for the help!
Positive
my husband ended up finishing it because he got frustrated with me. but thanks...
Positive
Great guy! Helps as much as he possibly can!

Customer Question

I have a Reznor V3 T Core2 mdl no UDAP45 garage heater that won't light. I control card has a lit solid green light that starts flashing green when it trys to light. What's wrong?

 

Optional Information:
Make : V3 T Core2 Power Vent
Model : UDAP45

Already Tried:
turned off power, turned off gas, waited 5 minutes then turned gas on, power on, raised thermostat . . . . would not start burner.

Submitted: 898 days and 3 hours ago.
Category: HVAC
Value: $38
Status: CLOSED

Accepted Answer

Picture
Expert:  Tom replied 898 days and 2 hours ago.


Tom :

Hi,, sorry you're having trouble with your Reznor...

Tom :

When it calls for heat...[green light flashing]...does the vent motor start? [small exhaust motor inside cabinet]

Customer :

Sorry for the delay in responding. Unit starting working again yesterday morning but then quit again yesterday afternoon. It is not working this morning. When the unit was working yesterday morning, it had an exhaust-like smell so I took the vent cap off and inspected. I didn't find any obstructions so I put the exhaust cap back on. Now . . . the answer to your question. I checked the unit this morning and when there is a call for heat, the vent motor does start and continue running. I watched the green light on the ic board and it flashes 3 times then there is a 1 second delay and then it repeats. Any ideas? I'm wondering if there is a clog in the natural gas line?

Tom :

3 flashes is an open hi limit switch or rollout switch open...The rollout on your 45 is a manual reset...so it wouldn't light again if it tripped until you reset it...

Tom :

The high limit is an auto reset so it would try to go again after it cooled down.

Tom :

Is this an old or new installation?

Tom :

How long does it run before it shuts down? Was the unit ever converted from natural to LP or vice versa... and does the main fan run OK?

Tom :

Sorry for the delay on my end also. Sorry for so many questions...I have to go but I'm going to opt out in case you're online another tech may be able to assist..He'll be able to see this dialog so you don't have to repeat everything. Otherwise I'll check in a little later. Thanks! Tom

Tom :

Hi,,just re read your post...if it won't light at all now ... and you're getting three flashes..it's probably an open limit switch. Check the wire connections to the limit and make sure they are good. Also check all plug in connections and in the wire harness.

Tom :

https://www.rezspec.com/cms_download.php?mod_files[fileid]=000000002602

Tom :

Here is a link to the install manual if you don't have one. Page 31 shows the location of the high limit sensor. You can pull the wires off and check for continuity with an ohm meter if you have one. If it's open circuited it will have to be replaced.

Tom :

We still need to figure out why it's tripping...were you able to see through the entire vent pipe? Also check the heat exchanger for cracks...(inspect through the front louvers) if it's been in service for awhile.

Thanks, Tom

Customer :

Tom -

Customer :

Sorry for the slow reply again. I had to work late yesterday and didn't get a chance to look at unit until this morning. Answers to your questions about the unit. I bought the house back in August so that's as far back as I know. House was built in 2005 and looks like the unit was new when the house was built. Unit has worked okay until recently (Sept - Present). I just checked the limit control and flame rollout switches with an ohm meter and both checked at 0.1 ohms. I noticed the thermal wrap on the flame rollout switch near the heat exchanger had slid off and was exposing the copper wire. I slide the thermal wrap over the exp0sed copper conductor and reinstalled the flame rollout switch. When I powered the unit up, it started working. Also, I visually inspected the heat exchanger and didn't find any cracks or rust . . . but quite a bit of dust which might be what I was smelling last time the unit was working. Anyway, I'd like to give the unit a day to see if it keeps operating. Can the limit switch work intermittently or do they usually fail once and quite working permanently?

Customer :

Tom -

Customer :

Heater is working fine now. Problem must have been bad electrical connnection to limit switches. Thanks for your help!

Expert TypeHVAC Technician
Category: HVAC
Pos. Feedback: 99.8 %
Accepts: 763
Answered: 11/27/2010

Experience: 16+yrs HVAC/R service. Residential Commerical Industrial

Ask this Expert a Question >
Picture
Expert:  Tom replied 894 days and 3 hours ago.

You're welcome..glad it's working..as for the limit...very seldom would one be intermittant..usually good or bad....you're correct..the wire connection was probably at fault..

 

Intermittant problems like that ...I usually start tugging on wires..cleaning connections..unplugging and replugging harnesses....good call..

 

Let me know if you need further assistance...feedback is appreciated and I will do the same. Thank you!

 

Tom

 
Tweet

4 HVAC Technicians are Online Right Now

Ask Your Question Now
Hvac Questions Date Submitted
I have an HVAC system that I want to convert to 2 zones. There 5/8/2013
I have a gas line that runs out the back wall of my home, goes 5/8/2013
I have a Trane XL 1200 heat pump manufacture date of 5/96. 5/8/2013
how do I get my honeywell programmable thermostat to reset? 5/8/2013
I have a goodman GPG13300701AA gas pack that will not heat. 5/5/2013
i want ot put a honeywell RTH8580 thermostat on my Trane WCH042C100AA 5/5/2013
Replacing White Rodgers A/C Thermostat, need same model 5/4/2013
I have a York Diamond 80 HVAC system. I was trying to change out the t 5/3/2013
I have a GMH950703BXAF Goodman 5/3/2013
four flashes on goodman c h&a and no fan so replaced limiter still 4 f 5/2/2013
RSS
Next 10 >
Ask A HVAC Technician
Type Your HVAC Question Here...
characters left:

Top HVAC Experts

See More HVAC Technicians

In The News

Nbc
Washington Post
New York Times
Cnn
Learn More

How It Works

  • Ask an Expert
  • Get a Professional Answer
  • Ask Followup Questions
  • 100% Satisfaction Guarantee
Learn More
 
 
 

Recent Articles in HVAC

  • Electric Boiler Problems
  • Radiant Heating Problems
  • Questions on Furnace Problems
  • Air Conditioner Questions
  • Questions about Expansion Tank Problems
  • Questions about Thermocouple Problems
  • Questions about Radiator Problems
  • Air Filter Problems
  • Dehumidifier Problems
All HVAC Articles
 
 
 
close
Find Expert answers related to your question.
Sign up using email
We will never post anything without your permission.
Already have an account? Sign in

Ask a HVAC Technician

Get a Professional Answer. 100% Satisfaction Guaranteed.
237 HVAC Technicians are Online Now
Type Your HVAC Question Here...
characters left:
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.
Truste
Contact Us | Terms of Service | Privacy & Security | About Us | Our Network
© 2003-2013 JustAnswer LLC
  • Pearl.com
  • JustAnswer UK
  • JustAnswer Germany
  • JustAnswer Spanish
  • JustAnswer Japan