Ask Matthew Your Own Question

Matthew
Matthew, HVAC Technician
Category: HVAC
Satisfied Customers: 1994
Experience:  14 years experience in the HVAC field of service, installation, Manual J & D calculations
Type Your HVAC Question Here...
Matthew is online now
A new question is answered every 9 seconds

RUUD UGPH12EARJR. Furnace not working. Can smell gas but

Resolved Question:

RUUD UGPH12EARJR. Furnace not working. Can smell gas but no flame. Followed instructions on side of furnace but no flame. killed power, turned gas to off, waited until no gas smell, turned it all back on, no flame.
Submitted: 3 years ago.
Category: HVAC
Expert:  Matthew replied 3 years ago.

Matthew :

Hello, My name is XXXXX XXXXX X will do my best to help you today.

Matthew :

Can you hear/see the sparker sparking?

Customer :

no, cant hear or see it

Matthew :

Is the inducer fan motor coming on? This is the small motor that the exhaust pipe hooks to

Customer :

when i turn the thrmostat to fan it runs/blows air. same thing?

Matthew :

no that is the circulating blower. The inducer motor comes on first during a heat call it pushes the exhaust out of the house. it is the small motor at the top of the furnace hooked to the exhaust pipe. I need to know if this is coming on like it should when you turn the thermostat to heat.

Customer :

ok ill go check. i dont hear much of anything though when i turn everything back on. ill go check

Customer :

small motor just above gas on/off switch is not running, i think its the one. cant hear anything else running

Matthew :

find the furnace control board located behind the bottom door. You will see where the thermostat wires hook to this board at terminals labeled with letters. You need to find a small piece of wire or paper clip and form a jumper/bridge that connects the W terminal with the R terminal then push in the door safety switch that this bottom door holds down when it's on and tell me if the inducer draft motor comes on this time.

Customer :

w/r bridged big fan board is on turned on

Matthew :

The big fan came on or the inducer came on?

Customer :

seemed like the fan the board was on turned on. inducer im guessing is connected to a 4" pipe?.

Customer :

my first time in a furnace sorry

Matthew :

your doing great.

Matthew :

The big fan (circulating blower) will come on for 90 secs after power interruption which happens when you take the bottom door off so keep the jumper in and hold the button down for a good 2 mins see if the circulating fan turns off and the inducer motor turns on.

Customer :

k

Matthew :

While you are doing this be mindfull of the LED's on the board tell me if they blink a number code.

Customer :

only circ fan comming on 4 blinks pause 4 blinks

Matthew :

Great. that is a closed pressure switch when it shouldn't be.

Matthew :

I'm going to send you some pictures...

Customer :

k

Matthew :

Full Size Image
This is a pressure switch

Customer :

k

Matthew :

There is a small hose that hooks this switch to the body of the inducer

Matthew :

Take the hose off the inducer and the pressure switch and blow through both ends.

Customer :

please tell me thats a inducer thank god

Customer :

be right back

Matthew :

Then take a small piece of wire or a paper clip and clean the small port on the inducer this hose slides over

Matthew :

hold on there is more

Customer :

k

Matthew :

Check for any water in the hose and let me know if the hose has water in it

Customer :

k

Matthew :

Pull it all back together and tell me if it still blinks 4 times

Matthew :

ok go

Customer :

k

Customer :

3 tiny drops of water when i blew through. inducer connection has minor rust but clear. pressure switch connection was clear. still 4 leds

Matthew :

This is the exact model number of the pressure switch for your furnace. You need a new one I'm afraid. This pressure switch should be open at all times then when the inducer motor starts up it pulls a vacuum on the switch and closes the contacts to prove that the furnace is exhausting

Matthew :

If you take one of the two wires off the pressure switch the inducer should fire right up. Once the inducer comes on you can plug the wire back up and the furnace will ignite. Once that heat call is over though the switch is still closed so the next time the furnace needs to come on it will not until you simulate an open pressure switch again by unplugging one wire.

Customer :

k ill try it

Matthew :

The water in the hose is probably the reason the switch went bad. You can try to blow into the switch and see if it jars loose

Matthew :

But once the switch starts to stick it will just do it again.

Customer :

k

Customer :

ill be right back

Matthew :

If unhooking one of the two wires doesn't reset the LED then the board is bad and is reading a closed pressure switch signal when there isn't one so you would need a new board. It is rare for this to be the case, but it is a possible scenario

Customer :

disconnecting 1 wire worked. got flame inducer and all

Matthew :

so you need a new switch. Like I said you will have heat until the next heat call comes then the same thing will happen all over again.

Customer :

looking at the switch now

Customer :

k

Customer :

too bad you cant open these things

Matthew :

yeah

Customer :

well is that it?

Customer :

if so thanks alot

Matthew :

That's it

Matthew :

If you call someone they are going to charge you $85 service call, $60 for the pressure switch, and 1/4 hr labor at $85/hr

Customer :

true

Matthew :

So if you can wait for the shipping your better off ordering one it is just two wires and youc an't get them reversed

Customer :

going to go put the switch back in

Matthew :

We get them for about 15-20 dollars wholesale that price online is about what a mark up would be if a service company sold you one

Customer :

ouch

Matthew :

Gotta make a living :)

Customer :

true

Customer :

be right back

Matthew :

what bothers me though is the water

Matthew :

Is the exhuaust pipe going up through the roof of the home or does it go out a side wall?

Matthew :

Water should not be in this exhaust pipe. If the pipe doesn't have rise and makes a hard turn or something causing the exhaust to get trapped it could condense the gas and form small amounts of condensation. If the cape on the end of the pipe outside has come loose or snow builds up around it and melts this is also bad it is suppose to be a minimum of 3' off the ground if horizontal and 1' over the roof peak if it goes out the roof.

Matthew :

cape=cap

Customer :

k

Customer :

it was litteral two tiny tiny drops and we have not got it serviced in two years. dont yell at me. but thanks ill check it out

Matthew :

I don't really believe in yearly service. Don't tell my customers that, but as long as you change the filter there isn't much service to be done. The stuff really either works or doesn't work going in once a year to check it isn't going to change when the parts go bad.

Matthew :

If you do not have a standing pilot furnace that produces rust there is no point in service

Customer :

hmm ok

Customer :

well i installed it and its working on its own

Customer :

without the trick

Matthew :

Hopefully it will not stick again

Customer :

but as you said ill know what to look for

Matthew :

That is basically what I would do on a service check. take the hose off blow through it, clean the port, clean the flame sensor with some sand paper, inspect for loose wiring, change the filter, and see if the igniter looks warn. That's about it.

Customer :

thanks i learned alot

Matthew :

Have a happy thanks giving

Customer :

you too

Matthew, HVAC Technician
Category: HVAC
Satisfied Customers: 1994
Experience: 14 years experience in the HVAC field of service, installation, Manual J & D calculations
Matthew and 3 other HVAC Specialists are ready to help you

JustAnswer in the News:

 
 
 
Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.
 
 
 

What Customers are Saying:

 
 
 
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
< Last | Next >
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
  • Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help. Mary C. Freshfield, Liverpool, UK
  • This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!! Alex Los Angeles, CA
  • Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult. GP Hesperia, CA
  • I couldn't be more satisfied! This is the site I will always come to when I need a second opinion. Justin Kernersville, NC
  • Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around. Esther Woodstock, NY
  • Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know. Robin Elkton, Maryland
 
 
 

Meet The Experts:

 
 
 
  • gotoman for ac's Avatar

    gotoman for ac

    HVAC Technician

    Satisfied Customers:

    4657
    51 years of experience install design and repair of all makes and models of AC
< Last | Next >
  • http://ww2.justanswer.com/uploads/SE/ServiceTechRus/2012-6-7_2119_056.64x64.JPG gotoman for ac's Avatar

    gotoman for ac

    HVAC Technician

    Satisfied Customers:

    4657
    51 years of experience install design and repair of all makes and models of AC
  • http://ww2.justanswer.com/uploads/AL/alumalite/2012-5-10_234018_shutterstock506249951forJA500.64x64.jpg Phil's Avatar

    Phil

    Mechanical Engineer

    Satisfied Customers:

    3888
    Retired HVAC/ Electrical & Boiler contractor. Industrial
  • http://ww2.justanswer.com/uploads/skibum0101/2008-12-16_015819_just_answer.jpg Rick Mather's Avatar

    Rick Mather

    HVAC Technician

    Satisfied Customers:

    3132
    35 years experience, HVAC
  • http://ww2.justanswer.com/uploads/RY/Rygis20/2011-5-7_3143_DSC5324.64x64.JPG Matthew's Avatar

    Matthew

    HVAC Technician

    Satisfied Customers:

    1994
    14 years experience in the HVAC field of service, installation, Manual J & D calculations
  • http://ww2.justanswer.com/uploads/KE/kentguidry/2011-9-26_214316_0059.64x64.jpg Kenton Guidry's Avatar

    Kenton Guidry

    HVAC Technician

    Satisfied Customers:

    962
    12 years install/service experience.
  • http://ww2.justanswer.com/uploads/solarman1947/2009-12-13_223915_phpkKBcXq_c2PM.jpg Rick Ridley's Avatar

    Rick Ridley

    UK Heating Engineer

    Satisfied Customers:

    871
    Retired But have had 30 years on the tools, Ex CORGI
  • http://ww2.justanswer.com/uploads/Ironheadfan/2009-12-18_222416_pump_005.jpg Tom's Avatar

    Tom

    HVAC Technician

    Satisfied Customers:

    770
    16+yrs HVAC/R service. Residential Commerical Industrial