I am working on a Honeywell RM7895 A 1014 burner control.

Customer Question

I am working on a Honeywell RM7895 A 1014 burner control. The unit goes through purge and begins to light the burner, but instead of allowing 10 seconds to see the pilot, it kicks out after 3 seconds which is not enough time for the pilot to light. It then begins the purge cycle again.
Submitted: 6 years ago.
Category: HVAC
Expert:  BillyHvac replied 6 years ago.

Is JR1 clipped and removed?

 

The JR1 in place is 10 sec...and clipped and gone (or defective) is 3 seconds

 

 



Edited by Billy on 11/1/2010 at 1:13 AM EST
Customer: replied 6 years ago.
No. We replace it with another burner control and have the same condition.
Expert:  BillyHvac replied 6 years ago.

 

So JR1 is in place and 3 second rectification is all you have?

 

 

Customer: replied 6 years ago.
JR1 is in place. Terminal 8 is only on for three seconds, instead of 10 seconds.
Expert:  BillyHvac replied 6 years ago.

 

What base are you using and amplifier, purge card?

 

Is everything new ?

 

 

Customer: replied 6 years ago.

We are using the same amplifier and purge card, so they are not new. The unit was running on Wednesday when we shutdown to make repairs. I don't think I have replacement purge cards or amplifier.

Expert:  BillyHvac replied 6 years ago.

 

Have you run a cycle in Test mode yet?

 

 

Customer: replied 6 years ago.
Not sure how to run a cycle in Test mode?
Expert:  BillyHvac replied 6 years ago.

 

See page 12 here.....run/test, if equipped is on top left

 

http://customer.honeywell.com/techlit/pdf/PackedLit/66-1090.pdf

 

Customer: replied 6 years ago.
Our model does not have the run/test switch.
Expert:  BillyHvac replied 6 years ago.

 

Ok,

 

given you have you changed control, I am betting purge card. Unfortunately these parts are real pricey.

 

But simply, if the old control and new control both fault at 4 sec instead of 10...the common denominator is purge card. If amplifier were bad it will still go 10 seconds then fault.

 

 

Customer: replied 6 years ago.
Is it possible the purge card could have been damaged during the rewiring?
Expert:  BillyHvac replied 6 years ago.

 

very much so. Electrical issues is the number one enemy of the card...even if ground is/was bad.