We have a tempstar 9000. When the t-stat engages, there is

Customer Question

We have a tempstar 9000. When the t-stat engages, there is a buzzing noise, and sometimes the burners ignite, but then it turns off.. any suggestions?
Submitted: 3 years ago.
Category: HVAC
Expert:  Tom replied 3 years ago.

Tom :

Hi, sorry you're having trouble with your furnace.

Tom :

Have you had the front off of the furnace to watch the burners ignite?

JACUSTOMER-klr1bjen- :

Yes.

JACUSTOMER-klr1bjen- :

It will ignite intermittently.

Tom :

Have you tried cleaning the flame sensor?

JACUSTOMER-klr1bjen- :

After aprox. 10 seconds it will kick the system off.

JACUSTOMER-klr1bjen- :

where is that located?

Tom :

I don't have a book on your exact furnace...are you near it? I can describe it for you.

JACUSTOMER-klr1bjen- :

I'll be there in 10 seconds.

Tom :

Ok!

JACUSTOMER-klr1bjen- :

Ok.

JACUSTOMER-klr1bjen- :

ready

Tom :

You described a buzzing noise when it starts...that is probably the spark ignition..[you don't see a bright orange ignitor when it lights do you?]

JACUSTOMER-klr1bjen- :

No. There is a 1.5" diameter window that you can see the flame through.

JACUSTOMER-klr1bjen- :

Most of the time there is just a buzzing noise for about 10 seconds, then silence for the next few minutes.

Tom :

Here is a pic of a typical flame sensor.

JACUSTOMER-klr1bjen- :

every once in a while the furnace will ignite without the blower engaging.

JACUSTOMER-klr1bjen- :

that will last aprox. 10 sec., then the whole cycle starts over again.

Tom :

Ok..the buzzing is the spark ignitor. You should see a couple of wires going up to the compartment where the burners are...

JACUSTOMER-klr1bjen- :

there are 4 red wires

Tom :

Are there screws holding a cover on the panel with the sight window?


 


 

JACUSTOMER-klr1bjen- :

the cover where the window is located has about 12 screws holding it on.

JACUSTOMER-klr1bjen- :

remove?

Tom :

Ok..you''ll need to remove them to access the flame rod..

Tom :

Here is what happens....

JACUSTOMER-klr1bjen- :

Ok. standby

Tom :

One end of the burner has the spark ignitor ...that lights it off...generally..at the other side of the burner compartment there will be a sensor or probe like the one I showed you...it senses the flame to make sure all of the burners have lit...

Tom :

If it gets a little dirty or corroded..it won't sense properly and it will keep shutting your unit down. By recycling the power it resets the ignition module so it can try again.

Tom :

You need to locate the sensor and clean it up with some fine sandpaper or steel wool.

Tom :

You may see one with a bend in it like this one...a small single wire connected.

JACUSTOMER-klr1bjen- :

Not seeing it.

JACUSTOMER-klr1bjen- :

Im looking at the back of the burners.

Tom :

It will be located in front of the burner nozzle where the flame comes out.

Tom :

The flame actually has to contact it.

JACUSTOMER-klr1bjen- :

I am seeing a white wire going to the ignitor.

Tom :

Ok...is there another wire anywhere in the direct area of the burners?

JACUSTOMER-klr1bjen- :

there are two red wires going into a small transistor looking part that is mounted above the burners, but it is not as long as the sensor that we had on our previous furnace.

Tom :

That is a temperature limit switch..

JACUSTOMER-klr1bjen- :

this one is about the size of a dime in diameter, and aprox .5" long

Tom :

No...we're looking for another probe that is directly in the path of the flame..

JACUSTOMER-klr1bjen- :

that's all i can see.

Tom :

Ok,,,it could be part of the ignitor assembly...but not usually...

Tom :

just one wire to the ignitor?

JACUSTOMER-klr1bjen- :

two red wires go to the ignitor

JACUSTOMER-klr1bjen- :

the other two are at the part I just described.

Tom :

What about the white one?

JACUSTOMER-klr1bjen- :

one red going in is spliced into the white. i.e. it's the ignitor wire

Tom :

does the ignitor look anything like this?

JACUSTOMER-klr1bjen- :

I'm familiar with the sensor from a previous furnace, but I don't see it here.

JACUSTOMER-klr1bjen- :

Could it be mounted about 1 foot above the burners?

Tom :

no...it will be directly in front of the burner...

JACUSTOMER-klr1bjen- :

there are two red wires attached to a blackbox aprox 2X3"

JACUSTOMER-klr1bjen- :

that's what I thought.

JACUSTOMER-klr1bjen- :

Let me try to attach a photo.

Tom :


That would help.... Sorry I don't have a breakdown of your furnace...

JACUSTOMER-klr1bjen- :

Crap, it wont let me upload.

JACUSTOMER-klr1bjen- :

has to be a url

JACUSTOMER-klr1bjen- :

one sec.

Tom :

Ok...no problem...I'm looking for some literature..

JACUSTOMER-klr1bjen- :

Tom, I uploaded to my website here http://thinairmedia.com/2010/10/28/furnace-problems/

Tom :

ok...let me see if I can get there....

JACUSTOMER-klr1bjen- :

Hopefully this helps

Tom :

Ok..2 reds are definately a temp limit..so we don't need to concern ourselves about those..

Tom :

Did the ignitor look like the one in the last pic I posted?

Tom :

A white porcelain base with a prong looking device?

JACUSTOMER-klr1bjen- :

It's possible, but it's facing away from me

Tom :

Or does it look like 2 metal rods (electrodes) that would spark?

JACUSTOMER-klr1bjen- :

It looks like one porcelain

JACUSTOMER-klr1bjen- :

no electrodes.

Tom :

Ok...if you looked in that window while it's lighting do you see a really bright orange glow?

JACUSTOMER-klr1bjen- :

what's baffling me is that I can't find the temp sensor.

Tom :

flame sensor

Tom :

Ok...so no other wires...just the 2 reds and the 2 to the ignitor?

JACUSTOMER-klr1bjen- :

correct

Tom :

Can you pull the wires away from the rubber gasket on the left a little and make sure one isn't hiding below the others?

JACUSTOMER-klr1bjen- :

There are only 4 going in.

JACUSTOMER-klr1bjen- :

I just updated my site with a photo of the lower area.

Tom :

Ok....hold on and i"ll check it..

JACUSTOMER-klr1bjen- :

I just added another.

JACUSTOMER-klr1bjen- :

the two red wires above the burner.

Tom :

Ok....the two above are the high limit for the heat exchanger...

Tom :

So...to answer 1 question...the ignitor does glow before the burners light?


 

JACUSTOMER-klr1bjen- :

I can't see it through the window, it's offset.

JACUSTOMER-klr1bjen- :

should I light the furnace with the access door off?

Tom :

It would be bright enough to light up the entire burner box..

Tom :

no...

Tom :

it won't light with the door off...

JACUSTOMER-klr1bjen- :

I'm not seeing anything orange prior to the burner lighting.

Tom :

There is a pressure switch that looks at burner compartment air pressure and won't let it go with the door off anyway..

JACUSTOMER-klr1bjen- :

hmmm

Tom :

Ok...there is probably another justanswer.com tech itching to answer this because he's more familiar with your furnace....I think I should opt out and see if I can get you a better answer...I think there is another tech or two still online...

Tom :

Sorry I wasn't more help....usually we can talk these things through...

JACUSTOMER-klr1bjen- :

ok.

JACUSTOMER-klr1bjen- :

what do I do now?

Tom :

I'm going to opt out..that will open your question up to other techs...if someone is online that can answer they will reply to this thread just as I did. He will be able to see our entire conversation which will help...

JACUSTOMER-klr1bjen- :

ok

JACUSTOMER-klr1bjen- :

Thanks tom..

Tom :

Thanks..and I'll see if I can find someone for you... Tom


Expert:  Douglas replied 3 years ago.
Hi, I'm Douglas and I am here to help you resolve problems with your heating and cooling equipment.

Tom definately gave it the old college try, kudos

Can I get an actual model number?
Customer: replied 3 years ago.
Hello Douglas,

It's a NULS100BH03

Customer: replied 3 years ago.
Any idea where the flame sensor is located on this model?
Expert:  Douglas replied 3 years ago.
Ok, it would appear that your furnace has the spark to pilot ignition system. This is to say, when there is a call for heat, the pilot sparks and ignites. The very rod that is providing the spark is also used as the flame sensor. It was a bad idea from the get go because a tech could not check the flame signal because he couldnt put his meter on something that produced a 5,000 volt spark one moment then a DC microamp signal the next.

Anyway. The first thing would be to check the ignitor wire for any nicks or abrasions which would and could ground the spark before it gets to the ignitor and if it got to the ignitor, not affect the returning flame signal. Inspec the porcelen insulator for any cracks or chips. Next look at the electrode itself and clean it with a piece of steel wool.

If all that is good, we need to examine the ground from the pilot burner to make sure all connectios are good. Then we need to validate that the ground is legit by measuring the voltage from Neutral to Ground. If any stray voltage exisits, the flame rectification process will not work correctly.

Finally, if all that checks out, you would replace the ignition module.

Frankly if I were going to replace that module, I would replace the ignitor at the same time.

Actually, with a furnace that old, as you can imagine documentation is harder and harder to come by. They didnt have PDF files back then. In the link provided, it has a troubleshooting chart for that furnace on page 6. You will see a hand written note that the flame signal should be .15 to .3 microamps. Back then I am not sure how many techs actually had meters to read this. Today most do and all should.

I'm certainly not trying to spend your money here but you could end up dumping a pretty stiff chunk of change into this furnace and it's still an old goat. This was from the beginning years of condensing gas furnaces and frankly they (all early condensing gas furnaces) were in need of improvement. They were really trying to get their arms around lower flue temps and combustion.
Expert:  Douglas replied 3 years ago.

JustAnswer in the News:

 
 
 
Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.
 
 
 

What Customers are Saying:

 
 
 
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
< Last | Next >
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
  • Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help. Mary C. Freshfield, Liverpool, UK
  • This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!! Alex Los Angeles, CA
  • Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult. GP Hesperia, CA
  • I couldn't be more satisfied! This is the site I will always come to when I need a second opinion. Justin Kernersville, NC
  • Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around. Esther Woodstock, NY
  • Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know. Robin Elkton, Maryland
 
 
 

Meet The Experts:

 
 
 
  • gotoman for ac

    HVAC Technician

    Satisfied Customers:

    4657
    51 years of experience install design and repair of all makes and models of AC
< Last | Next >
  • http://ww2.justanswer.com/uploads/SE/ServiceTechRus/2012-6-7_2119_056.64x64.JPG gotoman for ac's Avatar

    gotoman for ac

    HVAC Technician

    Satisfied Customers:

    4657
    51 years of experience install design and repair of all makes and models of AC
  • http://ww2.justanswer.com/uploads/AL/alumalite/2012-5-10_234018_shutterstock506249951forJA500.64x64.jpg Phil's Avatar

    Phil

    Mechanical Engineer

    Satisfied Customers:

    3888
    Retired HVAC/ Electrical & Boiler contractor. Industrial
  • http://ww2.justanswer.com/uploads/skibum0101/2008-12-16_015819_just_answer.jpg Rick Mather's Avatar

    Rick Mather

    HVAC Technician

    Satisfied Customers:

    3132
    35 years experience, HVAC
  • http://ww2.justanswer.com/uploads/RY/Rygis20/2011-5-7_3143_DSC5324.64x64.JPG Matthew's Avatar

    Matthew

    HVAC Technician

    Satisfied Customers:

    1994
    14 years experience in the HVAC field of service, installation, Manual J & D calculations
  • http://ww2.justanswer.com/uploads/KE/kentguidry/2011-9-26_214316_0059.64x64.jpg Kenton Guidry's Avatar

    Kenton Guidry

    HVAC Technician

    Satisfied Customers:

    962
    12 years install/service experience.
  • http://ww2.justanswer.com/uploads/solarman1947/2009-12-13_223915_phpkKBcXq_c2PM.jpg Rick Ridley's Avatar

    Rick Ridley

    UK Heating Engineer

    Satisfied Customers:

    871
    Retired But have had 30 years on the tools, Ex CORGI
  • http://ww2.justanswer.com/uploads/Ironheadfan/2009-12-18_222416_pump_005.jpg Tom's Avatar

    Tom

    HVAC Technician

    Satisfied Customers:

    770
    16+yrs HVAC/R service. Residential Commerical Industrial