My Goodman Furnace does not start up. LED light blinks three

Resolved Question:

My Goodman Furnace does not start up. LED light blinks three times. All drainage and pressure hoses are open and clear. Draft Inducer motor does not start, however. I tried jumping both pressure switches in the correct order and got the system to operate normally. I believe, then, that the draft inducer motor is faulty. Is this correct?
Submitted: 3 years ago.
Category: HVAC
Expert:  Billy replied 3 years ago.
Chat Conversation Started
Billy :

Hello,

First make sure the barbed fittings are also cleared that the tube attaches to...also make sure the vent pipe and intake pipe (if equipped) are clear. You may also want to remove the draft motor and make sure no straw , grass feathers etc are in blower wheel which cuts down on suction....

Customer :

I have inspected those fittings, they seem clear. Though I could take the motor off.

Customer :

My most immediate concern, though, is that the motor doesn't even seem to WANT to start up.

Billy :

Ok..I missed the "not" in inducer does not start....sorry.

Does it hum or get warm?

Customer :

That's ok...no, when the call for heat is relayed to the furnace, I can hear a "click" which I assume is the circuit board telling the motor to begin running. Nothing happens at that point, and the red light then flashes three times.

Billy :

Thank you....do have a meter to check voltage?...and have you felt the motor to see if humming or warm

Billy :

And is this first time starting this year?

Customer :

It definitely does not hum, let me check to see if warm. No, I don't have a volt meter, and yes, this would be the first time starting this year.

Billy :

Ok....sometimes..not always...the motor is seized from setting.....Here is what I would try...turn power off and remove the motor assembly. Make sure the blower wheel is clear of animals etc...then spin it a couple times. If careful...you can assembly in your hand and just "bump start" the unit with the power switch and see if fan spins.

Customer :

Fair enough, I will try that. By the way, the motor is not warm. It is cool / room temperature to the touch.

Billy :

If possible. you could get a cheap 2 wire 120v tester and see if the plug that goes to the motor has 120v

Customer :

OK, the motor is not warm or humming, and the fan is not obstructed. The fan actually spun quite easily by hand when I did that, but does not fire up when connected back to the furnace. I "jiggled" the wiring connections and it still does not start up. I will get a 120v tester this afternoon and let you know about that.

Billy :

excellent...that will be the deciding factor. I wish you luck!

Customer :

Hi, again - I can't tell if the motor has 120v or not - when I hook the multimeter up and turn on the furnace, the reading spikes for a second (to as much as 80 or so) and then goes back down to 0. Does that sound right? Just want to be sure I was using the meter correctly.

Billy :

Do you have set for volts ac with ~ac voltage symbol and a value of 200 or less

Billy :

I just want to make sure we pick between the inducer motor or ciruit board correctly. You can test the meter by testing a working outlet for 120v

Customer :

Yes, the meter is set to ~ac @ 200 (lowest it goes). Just tried it again for good measure and it spikes between 17 and 80 and then goes back to 0. Tried the meter on a working outlet and it always stays at zero.

Billy :

so on a working outlet you do not get 120v?

Billy :

lets try it on L1 and COM on the circuit board with door switch taped down and power on

Customer :

My apologies - I had the meter configured incorrectly. I just tested on the wall outlet and got 120.7v. Tried again on the motor connection and it does the same - spikes up to 80 or so (sometimes lower) and then back to 0.

Customer :

I looked at the circuit board and couldn't determine exactly where to connect the meter, so I tried a mix of locations of inbound / outbound wires (the ones colored white, yellow, green, etc). Seems most read about 70v, with the occasional one reading 0.

Billy :

great...now are you familiar with the thermostat wire connections? R, Y, W, G and C

Customer :

yes, for what it's worth, mine only has R,Y,G,and W.

Billy :

yes,,then you have a blue wire I believe that attaches to a wire from outdoor ac unit

Customer :

yep

Billy :

that is "common"...now we need to see what the voltage is from "common" to R

Customer :

at the thermostat?

Billy :

at the circuit board in furnace

Customer :

oddly enough the blue wire in the furnace isn't connected to anything...and it doesn't look like it ever was. The sheathing is still completely on it (never been stripped) and it's twisted around itself.

Billy :

no air condition?

Customer :

No, we have A/C, and I just tested it again to be sure. It works fine.

Customer :

All the connections at the furnace (where the wires come onto the circuit board) measure right about 70v, with the exception of any of them connected to Yellow, which only measures about 27v.

Billy :

Thank you.....I am not trying to waste your time....I just want to be sure....there is a hot wire that comes into the furnace and goes to the door safety switch, and then leaves door safety switch and attaches to the circuit board. Do you know what I refer to?

Customer :

No, believe me, at this point I'm worried about wasting YOUR time!

Customer :

And yes, I can see that wire.

Billy :

put one meter lead to that wire...and the other meter lead to ground..or metal cabinet...tell me what we read

Customer :

121.9v

Billy :

Great.....now unplug the plug to inducer and do the best you can to see what the power is when inducer is to start.

Billy :

power to the inducer

Customer :

Ok, here's what I got: there are two wires leading to the inducer. One is black/gray, one is white. There is also a green (ground, I assume) leading from the inducer to the metal wall of the furnace. The black and white wires each have a connector mid-wire. I separated the connector for black and tested it with the furnace on. It reads 0v. Then put back the black wire and did the same with the white. It also reads 0v. By chance are we moving toward a problem with the control board?

Billy :

you are correct.....If there is 24v present at W terminal where the white thermostat wire attaches....and anything short of 115v going to inducer motor, then we have a bad circuit board. It was kind of my hunch but I hate to see a couple hundred spent on a new motor and still not work...

It appears to be a bad circuit board. I do not know how much tinkering you are comfortable with...but if you want to get 120v to the inducer..either with ext cord or from board...you can test the motor...It can also be benched tested by removing and wiring to 120v to see if it runs....but at this point I find it safe to say the circuit board is bad

Customer :

ah, very good. I am fine tinkering - just one quick confirmation, though: exactly which connection would I make to test the motor? from the safety switch to the motor, then?

Billy :

now you got it...yep....

Customer :

perfect, hey thanks so much for your help!

Billy :

You are very welcome...if you need further help let me know.







Billy, HVAC Technician
Category: HVAC
Satisfied Customers: 19649
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Billy and 2 other HVAC Specialists are ready to help you

JustAnswer in the News:

 
 
 
Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.
 
 
 

What Customers are Saying:

 
 
 
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
< Last | Next >
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
  • Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help. Mary C. Freshfield, Liverpool, UK
  • This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!! Alex Los Angeles, CA
  • Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult. GP Hesperia, CA
  • I couldn't be more satisfied! This is the site I will always come to when I need a second opinion. Justin Kernersville, NC
  • Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around. Esther Woodstock, NY
  • Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know. Robin Elkton, Maryland
 
 
 

Meet The Experts:

 
 
 
  • gotoman for ac

    HVAC Technician

    Satisfied Customers:

    4657
    51 years of experience install design and repair of all makes and models of AC
< Last | Next >
  • http://ww2.justanswer.com/uploads/SE/ServiceTechRus/2012-6-7_2119_056.64x64.JPG gotoman for ac's Avatar

    gotoman for ac

    HVAC Technician

    Satisfied Customers:

    4657
    51 years of experience install design and repair of all makes and models of AC
  • http://ww2.justanswer.com/uploads/AL/alumalite/2012-5-10_234018_shutterstock506249951forJA500.64x64.jpg Phil's Avatar

    Phil

    Mechanical Engineer

    Satisfied Customers:

    3888
    Retired HVAC/ Electrical & Boiler contractor. Industrial
  • http://ww2.justanswer.com/uploads/skibum0101/2008-12-16_015819_just_answer.jpg Rick Mather's Avatar

    Rick Mather

    HVAC Technician

    Satisfied Customers:

    3132
    35 years experience, HVAC
  • http://ww2.justanswer.com/uploads/RY/Rygis20/2011-5-7_3143_DSC5324.64x64.JPG Matthew's Avatar

    Matthew

    HVAC Technician

    Satisfied Customers:

    1994
    14 years experience in the HVAC field of service, installation, Manual J & D calculations
  • http://ww2.justanswer.com/uploads/KE/kentguidry/2011-9-26_214316_0059.64x64.jpg Kenton Guidry's Avatar

    Kenton Guidry

    HVAC Technician

    Satisfied Customers:

    962
    12 years install/service experience.
  • http://ww2.justanswer.com/uploads/solarman1947/2009-12-13_223915_phpkKBcXq_c2PM.jpg Rick Ridley's Avatar