I have a Coleman 3400-815. It no longer works in auto mode.

 
freon's Avatar
  • Answered by:freon
  • Licensed A/C Contractor
  • Positive Feedback: 100.0 %
  • Accepted Answers: 214
Verified Expert
in HVAC

Recent Feedback

Positive
Very helpful
Positive
Sorry about the delay. I accepted, and got booted off the internet at the same...
Positive
Thank you!Jolanta
Positive
he was a big help. Thank you for very much. If we have any more problems we will...
Positive
Well done thank you! I spoke with my contractor at your suggestion and I feel a...
Positive
Good, thorough, quick answers!
Positive
Great knowledge, very helpful.
Positive
good guy informative
Positive
Very knowledgable
Positive
THANKS SO MUCH. I APPRECIATE THE DETAIL OF YOUR ANSWERS. IT MADE IT MUCH EASIER...

Customer Question

I have a Coleman 3400-815. It no longer works in auto mode. I can manually switch it to "on" at the furnace, but it only blows cold air. I replaced the thermostat to see if that would help, but it still won't come on unless I use the furnace switch. I have a good multimeter, the wiring diagram, and plenty of automotive electrical experience, but don't have a clue about my furnace. Please help. Nicole

 

Optional Information:
Make : Coleman
Model : 3400-815

Already Tried:
new thermostat

Submitted: 1170 days and 14 hours ago.
Category: HVAC
Value: $15
Status: CLOSED
Picture
Expert:  freon replied1170 days and 14 hours ago.

Dear Nicole,

 

Please stand by while i draw up some info on your furnace. From your comments i gather that the heat is not working... but you are able to get the blower on. is this correct?

 

freon

Customer replied1170 days and 14 hours ago.

correct

 

Picture
Expert:  freon replied1170 days and 13 hours ago.

Nicole,

 

Can you do a check for me? Can you open your tstat exposing the wire terminals, put your tester on A/C volts and test between R and W. See if you have 24 to 28 volts.

 

Do this while i am gathering more info. please!

 

freon

Customer replied1170 days and 13 hours ago.

29.40

Picture
Expert:  freon replied1170 days and 13 hours ago.

Nicole! your wonderful! so fast! Ok... i have been on line and have not located your electrical schemematic yet. I wanted to make sure you didnt blow a fuse or something.

 

now... can you disconnect the red wire and put it with the white wire? Try this and see if you get the heat to come on.

 

freon

Customer replied1170 days and 13 hours ago.

I held the wires together, it did not come on.

Picture
Expert:  freon replied1170 days and 13 hours ago.

ok.

 

did you see some breakers on your electric furnace? if you do then turn them both off. snapping them real hard. Stand to the right or left and turn away snapping them one at a time real hard on. I know this sounds weird but this is how we electricians do just in case there is a flash. Now i was talking about breakers on the unit it self not the circuit breaker panel.

 

freon

 

Customer replied1170 days and 13 hours ago.

I can't find any breakers on the furnace.Would they be in the front under the panel? According to the wiring diagram I have the thermostat, fan switch, transformer, blower, fuse and disconnect assy., sequencers, limit switches, and heating elements. Hope this helps some.

Picture
Expert:  freon replied1170 days and 12 hours ago.

Yes they must be fuses then and they are under the panel... now if you go in there be real careful... You need to check the fuses. to see if any are burnt open. This could be if you left the filter dirty to long or there is a fault in the heater elements. Can you do this?

 

The best and easiest way is to do it hot while checking with your meter... this way you dont have to pull any out unless they are burnt. just take your meter leads and put one on one end and one on the other end of the fuse where its made of metal. Now dont touch any of this stuff with your hands! its 240volts. Make sure you put your meter on the higher voltage scale. If you decide to check the fuses hot, see if you get a voltage when you test each one, top and bottom. if you get a zero or a few volts the fuse is good. if you get a 240volts the fuse is bad...understand?

 

freon

Customer replied1170 days and 12 hours ago.

Ok, that was a bit scary. All 4 fuses are good and tested around .008

Picture
Expert:  freon replied1170 days and 12 hours ago.

AWESOME!

 

You're doing great...So you have good voltage on tstat and fuses... i think what you have out is called the sequencers but i cant understand how both sets can be bad at the same time unless they went out over a period of time and you didnt notice.

 

Now i dont know how many heat strips you have but you have 4 fuses so you may have as many as 4 heat strips. can you tell me if you see a 60 amp on each fuse?

 

freon

Customer replied1170 days and 12 hours ago.

I just moved in a few months ago and the furnace never seemed blow as warm as I thought it should (if that helps at all).

 

I have (2) 60amp and (2) 30 amp fuses. From the wiring diagram, it appears I have 3 heating elements

Picture
Expert:  freon replied1170 days and 12 hours ago.

ok,

 

from your fabulous help i believe you have 15 kw heat. now this means you more than likely have one single pole sequencer and 1 double pole sequencer... these must be out if nothing comes on when you turn the heat on at the thermostat... be sure the tstat has been switched to electric heat...check tstat manual for this.

 

now let me get a picture of the sequencers for you:

 

now this is what i think you have

 

but on the same plate like this:

 

is this correct or is it like the one to the left?

 

freon

Customer replied1170 days and 12 hours ago.

The images are vertical so I'm not sure what you mean by the one on the left. It looks like I have 2 on the same plate, one single and one double. Are there stores that might sell these or do I need to order replacements online? Anything I need to know about replacing them?

Picture
Expert:  freon replied1170 days and 12 hours ago.

Ok,

 

look and see if yours match any of the pictures. Yes you can buy on line or at a local store... what city are you in?

 

freon

Customer replied1170 days and 12 hours ago.

The pics of each sequencer matches except my shorter one has 4 prongs on the bottom (2 on each side) and 2 prongs on top (1 on each side) so missing 1 top prong. The taller seq. matches except the top has 3 prongs (1 on one side and 2 on other) rather than 4 in the pic. I hope this makes sense.

 

I am in Monroe, WA

Picture
Expert:  freon replied1170 days and 11 hours ago.

yes it does... now i am positive you have 15 kw heat... it is either going to be the sequencer or the fan switch... we dont want you to buy parts you dont need so we have to look for the problem... are you willing to keep checking?

 

freon

Customer replied1170 days and 11 hours ago.

Sounds good. What should I check next?

Picture
Expert:  freon replied1170 days and 11 hours ago.

ok,

 

on the double stack sequencer, you must check the lower wire connections with your volt meter to see if it is getting a signal of 24 to 29 volts. Do you have a black wire on one side and a white wire on the other ?(on the bottom stack of the double sequencer)

 

freon

 

be careful it might be a tight squeeze in there!

Customer replied1170 days and 11 hours ago.

I do have a black wire and white wire. Do I put one lead on the blk and one on the wht?

Picture
Expert:  freon replied1170 days and 11 hours ago.

yes! youre good.

 

But make sure the tstat is calling for heat and the temperature is up!

 

look for 24 to 29 volts. the upper stacks have 240 volts so be careful!!!

 

freon

Customer replied1170 days and 11 hours ago.

Looks good, 25.9

Picture
Expert:  freon replied1170 days and 11 hours ago.

ok,

 

now, put your meter leads on the top two wire connections and tell me if after 60 seconds if you have a reading of 0 or 240volts?

 

freon

 

now do this with a call for heat and all.

freon40273.9076415509

Customer replied1170 days and 11 hours ago.

I'm not sure which top two wires you mean. On the same seq. I have 2 wires on the next level (2 reds) and 3 wires on the top level (2 yellow 1 grey).

Picture
Expert:  freon replied1170 days and 11 hours ago.

Sorry about that... on the top level or stack what ever you want to call it... the voltage goes across horizontally on these sequencers... the bottom is 24 v and the next two levels or stacks are 240 volts, lets check the top level put one lead on the yellow with the other lead on the other yellow across from the first. then do the same with the red wires...let me know what the voltage is for each...remember to wait 60 seconds or so for the sequencer to switch (if it was really a working unit).

Customer replied1170 days and 11 hours ago.

No problem, you have been great. I got 238.5 for both and remained right about the same for the entire 60 sec.

Accepted Answer

Picture
Expert:  freon replied1170 days and 10 hours ago.

Ok this is wonderful!! why because you just told me that the bottom of the sequencers have 24 volts and the top you are reading 230 something volts, which is the same as saying that the sequencer is not operational! if it was working you would see a zero or there abouts on the two red wires and a zero on the two yellow wires. Now i believe the other sequencer is bad also so just replace em both. You can find your parts on line at

Americanhvacparts.com or your nearest parts house. just look up air conditioning at whitepages.com for your city or zip. call em before you go to make sure they will sell it to you.

 

freon.

Expert TypeLicensed A/C Contractor
Category: HVAC
Pos. Feedback: 100.0 %
Accepts: 214
Answered: 4/5/2010

Experience: 22 years Licensed Contractor State of Texas

Ask this Expert a Question >
Customer replied1170 days and 10 hours ago.

Thank you so much for all your help! You have been fantastic. I couldn't possibly afford to have a repair person come out, so I really appreciate it. Now my kids and I can finally get some heat. Thank you so much.

Customer replied1170 days and 10 hours ago.

Thank you so much for all your help! You have been fantastic. I couldn't possibly afford to have a repair person come out, so I really appreciate it. Now my kids and I can finally get some heat. Thank you so much.

Picture
Expert:  freon replied1170 days and 10 hours ago.

That is so wonderful that you did all that. I am really proud of you. Now be sure when you change out the parts you turn the breaker off and tape it off with duct tape... i dont want anyone to turn it on while you are working on it. (kids) Take and make a drawing of the wires and where they go. so you can put them back on the right spot. Later if you get mixed up just give us another question and request me.

 

Is there anything else i can help you with? If not you may click on ACCEPT.

 

Thank you so much for contacting Just Answers! we appreciate you very much!

 

freon

 
Tweet

HVAC Technicians are Online Right Now

Ask Your Question Now
Hvac Questions Date Submitted
I have a Carrier HVAC system. Tech2000 SS. Last night it quit 6/12/2013
My son just moved in today to a house in Georgia where it is 6/11/2013
I've struggled with McQuay Enfinity Water Source Heat Pumps 6/2/2013
Bryant HVAC units, one for downstairs doesn't blow cold air, 5/31/2013
Turn on A/C without memory card? 5/28/2013
My white rogers thermostat type # XXXXX is flashing HVAC 5/20/2013
I have a Trane HVAC 5/19/2013
Hello, I have an existing Copeland Compressor for my HVAC system, 5/16/2013
I am a service tech with 49 yrs. experience in all genre of 5/15/2013
We have a Carrier 376BAW060115 model furnace. We have not used 5/12/2013
RSS
Next 10 >
Ask A HVAC Technician
Type Your HVAC Question Here...
characters left:

Top HVAC Experts

See More HVAC Technicians

In The News

Nbc
Washington Post
New York Times
Cnn
Learn More

How It Works

  • Ask an Expert
  • Get a Professional Answer
  • Ask Followup Questions
  • 100% Satisfaction Guarantee
Learn More
 
 
 

Recent Articles in HVAC

  • Electric Boiler Problems
  • Radiant Heating Problems
  • Questions on Furnace Problems
  • Air Conditioner Questions
  • Questions about Expansion Tank Problems
  • Questions about Thermocouple Problems
  • Questions about Radiator Problems
  • Air Filter Problems
  • Dehumidifier Problems
All HVAC Articles
 
 
 

Ask a HVAC Technician

Get a Professional Answer. 100% Satisfaction Guaranteed.
72 HVAC Technicians are Online Now
Type Your HVAC Question Here...
characters left:
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.
Truste
Contact Us | Terms of Service | Privacy & Security | About Us | Our Network
© 2003-2013 JustAnswer LLC
  • Pearl.com
  • JustAnswer UK
  • JustAnswer Germany
  • JustAnswer Spanish
  • JustAnswer Japan