Lower element of electric hot water heater does not come on.

Customer Question

Lower element of electric hot water heater does not come on. Lower thermostat checks OK. Upper element come on for demand, but connection 4 that feeds lower thermostat tests open. Both thermostats are set at 130F.
Submitted: 5 years ago.
Category: HVAC
Expert:  plumber 171 replied 5 years ago.

have you checked to see if the element has continuity. from what you are saying the lower stat works fine but it wont heat thats beacuse the element is bad. if your heater is known for high scale it will build up around the element causing it to over heat and burn out shut off the power to the heater and disconect both wiers to the element and test for continuity if no sound the element is bad

 

i recomend if the heater is old 5 years of bettter replace both upper and lower stats as well as the upper and lower elements

Customer: replied 5 years ago.
I have replaced both upper and lower elements even though both older elements checked OK. New elements checked OK for continuity. Replaced both upper and lower thermostats (Apcon style). All connections check OK except upper thermostat #4, the feed from the upper thermostat to the line side of the lower thermostat. That line is not "hot" and the heating element is not energized. By the way the old upper and lower thermostats showed the same condition, even though the water heater had been performing properly for over one year.
Customer: replied 5 years ago.
Awaiting reply from plumber 171. Answer he provided was what I already knew or had done. Need specific answer for why upper thermostat is not working as expected.
Expert:  plumber 171 replied 5 years ago.

it is verry possible the line became broken in the jacket this can happen if it over heats the wire gets brittle and breaks. if the heater is older then 5 years get a new on ( just recomendation ) if not and you have electrical ( sounds like you do ) fish a new wire down to the element but first try to test for continuity from the upper stat wiers to the lower stst wiers first

 

one more thing is there a reset button on your lower stat ( they are usualy on the upper one ) if so see if it triped first

Customer: replied 5 years ago.
Checked continuity of black wire from connection 4 on upper thermostat to connection 1 of lower thermostat - checks OK. Problem seems to be that connection 4 on upper thermostat is not energized when cold water heat demand occurs. Have rechecked wiring, continuity, and reset button several times. Tried to reverse connection 4 for upper element with lower thermostat connected to connection 3. Lower element was energized, but upper element was open (not energized). Tried to understand how upper thermostat functions internally, could not find any information in that detail. Still believe that upper thermostat connection 4 should be energized when cold water demands heat function. Really hope you can help me understand this problem, I would like to pay you for your usable advice.
Expert:  plumber 171 replied 5 years ago.

most electric heaters the top element heats up first then the lower they usualy never heat up at the same time first the top goes on then the botttom goes on afeter it senes temp

Customer: replied 5 years ago.
Sorry for the delay in response. I just now checked the heater thermostats again. Even though the unit has been on demand for over 3 hours, lower element still is not energized (connection 4 is open) and the outcoming water is barely luke warm (estimate between 80-90F.
Expert:  plumber 171 replied 5 years ago.

does the upper stat have a jumper between any of the tyerminals

 

Customer: replied 5 years ago.
Facing the front of the upper thermostat with the red reset button at the top, there are four connections on the left side and three connections on the right side. The top two connections, right & left, are for the 240 single phase line feed. The middle two left connections have a factory installed shorting bar and no connecting wiring. The bottom left connector has a yellow wire to the upper heating element. The middle connector on the right side has the blue wire to the upper element and the red wire to the lower element. The lower connector (#4) has a black wire going to the line side of the lower thermostat. The load side of the lower thermostat is a black wire completing the circuit to the lower element.
Expert:  Mark Henley replied 5 years ago.

Hi,

 

What are the stats set at ?

 

Thanks

 

Mark.

Customer: replied 5 years ago.
Both upper and lower thermostats are set at 130F.
Expert:  Mark Henley replied 5 years ago.

Hi,

 

Try turning the lower one up all the way to see if we can get it to come on.

 

Thanks

 

Mark

Customer: replied 5 years ago.
Mark,
I have reset the lower thermostat to 150F. Lower element did not energize, connector 4 lead from upper thermostat remained off. Then reset lower theermostat to 130F and upper thermostat to 150F. Still no response.
Really suspect problem is output at connector 4 of upper thermstat. Don't understand why old and new thermostats exhibit same condition. Again all wiring checks out to circuit diagram.
Customer
Expert:  Mark Henley replied 5 years ago.

Hi,

 

OK I'm understanding that terminl 4 is the lower right side terminal on the upper stat ?

 

Is that right ?

 

There is a reset on each stat or just the upper ?

 

Thanks

Customer: replied 5 years ago.
Mark,
Terminal 4 is the lower right side connector on the upper thermostat, it serves as the feed to the line side input to the lower thermostat which has only two connections, no reset button. Only the upper thermostat has a reset button.
Expert:  Mark Henley replied 5 years ago.

Hi,

 

OK then heres what is happening, just had to make sure you had the typical setup.

 

, the red reset button should kill both circuits and both legs of power.So if one element works they both will.

 

The jumper bar jumps power from the limit switch to the upper thermostat. then if the sensed water is cool the upper thermostat will energize the upper element and hold the lower one off until the thermostat opens ( temp rises on upper element ) .

 

When it opens it sends power down to the lower thermostat and if the lower is calling it will energize the lower element. On a cold tank of water you won't get both elements. How long did you leave it sit after changing the elements ?

 

Thanks

 

Mark.

Expert:  Mark Henley replied 5 years ago.

Hi,

 

I know it sounds back wards of how you would think it would work but thats how it works but both elements don't work at the same time on your heater. If you turn the upper one down as low as it will go and the lower one up as far as it will go and let it brew for a little while you'll see the lower stat energize when the upper satisfies.

 

What was your initial problem ?

 

Thanks

 

Mark.

Expert:  Mark Henley replied 5 years ago.

Hi,

 

 

I found a diagram of it. It shoud graphichelp explain what I'm trying to say.

 

 

Expert:  Mark Henley replied 5 years ago.

Hi,

 

Here's where I'm going with this, there is a chance that the elements and the thermostats were not the problem to begin with. Your initial conditions sound like it was the dip tube in the tank , it sounds like it broke off sending all the new cold water to the top of the tank instead of the bottom. Therefore , when you would run water the hot water would seem to run out real fast because the cold water was barely being heated before it short circuited to the leaving pipe. All the while you probably had hot water at the bottom of the tank. Even now you will probably still have the same problem until you replace the dip tube.

 

Thanks

 

Mark.

Mark Henley, Journeyman Technician
Category: HVAC
Satisfied Customers: 3217
Experience: UA Journeyman Pipefitter , HVAC, Refrigeration, DDC controls. 26 years.Commercial & residential
Mark Henley and other HVAC Specialists are ready to help you
Customer: replied 5 years ago.
Mark,
I have been working on this problem since 8:00 AM (EST). I had to step away from the computer for a while, then found 4 responses from you. The arguments about thermostatically sequencing the elements makes sense. The wiring diagram was helpful for understanding upper thermostat function and for that I will accept the answer, even though it doesn't fully solve the problem. The broken dip tube seems a logical issue, and makes sense. I will need to empty the tank tomorrow and pull the cold water pipe/dip tube (if I can) to see if your latest rational is right.Customer
Customer: replied 5 years ago.
I seem to have lost plumber 171 halfway through this exchange. Mark's replies really helped me to understand the nuances of the problem, especially the possibility of the broken dip tube which I will pursue tomorrow. If this information resolves the problem I will report back to your site. Thanks;

Van
Expert:  Mark Henley replied 5 years ago.

HiCustomer/p>

 

There was some trouble in getting back to you.

 

The diagram is typical of a two element single phase residential water heater, they don't operate in unison or simultaneously. Just had to verify that with how many limits you had and where the terminals were. I think you will probably find that your dip tube is broken off tomorrow. If not them its really just a matter of the tank being scaled up. Either way though let us know how it turns out.

 

Thanks

 

Mark.

Customer: replied 5 years ago.
Mark Henley,
I removed the cold water dip tube and found a small (5/32" diameter) hole about 4" from the inside top. The hole was so perfectly round and free of burrs or tears that I am not certain that it wasn't provided at manufacture. I also found the bottom 8" of the tank filled with lime. The lime had congealed into large lumps which proved difficult to remove. Considering the age and condition of the tank, frequent outages requiring replair, and this sort of indeterminate problem, I decided to replace the entire water heater. Did so and now we have hot water. Thanks for your advice. I believe I have found now an exellent source for home maintainence advice.

Van
Expert:  Mark Henley replied 5 years ago.

Hi Van ,

 

Glad I could help.

 

Thanks

 

Mark.

JustAnswer in the News:

 
 
 
Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.
 
 
 

What Customers are Saying:

 
 
 
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
< Last | Next >
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
  • Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help. Mary C. Freshfield, Liverpool, UK
  • This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!! Alex Los Angeles, CA
  • Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult. GP Hesperia, CA
  • I couldn't be more satisfied! This is the site I will always come to when I need a second opinion. Justin Kernersville, NC
  • Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around. Esther Woodstock, NY
  • Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know. Robin Elkton, Maryland
 
 
 

Meet The Experts:

 
 
 
  • gotoman for ac

    HVAC Technician

    Satisfied Customers:

    4657
    51 years of experience install design and repair of all makes and models of AC
< Last | Next >
  • http://ww2.justanswer.com/uploads/SE/ServiceTechRus/2012-6-7_2119_056.64x64.JPG gotoman for ac's Avatar

    gotoman for ac

    HVAC Technician

    Satisfied Customers:

    4657
    51 years of experience install design and repair of all makes and models of AC
  • http://ww2.justanswer.com/uploads/AL/alumalite/2012-5-10_234018_shutterstock506249951forJA500.64x64.jpg Phil's Avatar

    Phil

    Mechanical Engineer

    Satisfied Customers:

    3888
    Retired HVAC/ Electrical & Boiler contractor. Industrial
  • http://ww2.justanswer.com/uploads/skibum0101/2008-12-16_015819_just_answer.jpg Rick Mather's Avatar

    Rick Mather

    HVAC Technician

    Satisfied Customers:

    3132
    35 years experience, HVAC
  • http://ww2.justanswer.com/uploads/RY/Rygis20/2011-5-7_3143_DSC5324.64x64.JPG Matthew's Avatar

    Matthew

    HVAC Technician

    Satisfied Customers:

    1994
    14 years experience in the HVAC field of service, installation, Manual J & D calculations
  • http://ww2.justanswer.com/uploads/KE/kentguidry/2011-9-26_214316_0059.64x64.jpg Kenton Guidry's Avatar

    Kenton Guidry

    HVAC Technician

    Satisfied Customers:

    962
    12 years install/service experience.
  • http://ww2.justanswer.com/uploads/solarman1947/2009-12-13_223915_phpkKBcXq_c2PM.jpg Rick Ridley's Avatar

    Rick Ridley

    UK Heating Engineer

    Satisfied Customers:

    871
    Retired But have had 30 years on the tools, Ex CORGI
  • http://ww2.justanswer.com/uploads/Ironheadfan/2009-12-18_222416_pump_005.jpg Tom's Avatar

    Tom

    HVAC Technician

    Satisfied Customers:

    770
    16+yrs HVAC/R service. Residential Commerical Industrial