Login|Contact Us
Question and Answer

HVAC

Ask a HVAC Question, Get an Answer ASAP!

  • Ask A Question
  • Browse Answers
  • Meet The Experts
  • How JustAnswer Works

Honeywell TH8000 install

 
Kenton Guidry's Avatar
  • Answered by:Kenton Guidry
  • HVAC Technician
  • Positive Feedback: 98.8 %
  • Accepted Answers: 962
Verified Expert
in HVAC

Recent Feedback

Positive
Very helpful, courteous and patient.
Positive
Just got fast start kit installed last weekend and it seems to have cured the...
Positive
Thanks so much for your help. I spent 3 hours online trying to find those...
Positive
Knows his stuff.
Positive
Very helpful. Provided me with an answer to my question where no one in this...
Positive
advice was well appreciated
Positive
Very informative session and very nice person: patient, helpful, courteous.
Positive
Kenton was great. He was incredibly patient with me and not only directed me...
Positive
Good feedback!

Customer Question

I am replacing my Honeywell Chronotherm III with a Honeywell TH8000.

The wall plate of the Chrom III is wired as follows
top row (8 terminals/slots)
#1 - Empty
#2 - Red
#3 - Green
#4 & 5 - Empty
#6 - Purple
#7 & 8 Empty

3 Row 8 terminals/slots
#1 thru 4 Empty
#5 - Black
#6 - White
#7 - Orange


5 Row 1 terminal/slot
#1 - Green

I am not sure which wires from the scheme above go to what terminals on the TH8000

Submitted: 1587 days and 10 hours ago.
Category: HVAC
Value: $15
Status: CLOSED
Picture
Expert:  Mark Henley replied1587 days and 10 hours ago.

Hi,

 

Are there any letter designations on the existing stat's terminals ?

 

The numbers and rows don't tell us enough.

 

Thank you,

 

Mark..

 

 

 

Customer replied1587 days and 10 hours ago.

On the Chromotherm III no there are no or designations

On the TH8000 there are:

 

On the left (facing the wall plate) Interior and exterior terminals

S1

S2

 

On the right (facing the wall plate) left interior top to bottom (I believe this is for conventional)

RC

R

W

Y

G

C

 

On the exterior of the terminal block (I believe this is for Heat Pump which I have)

RC

R

O/B

Y

G

C

 

Over the top of the left and Right terminal block are Arrows indicating the exterior is "Heat Pump" (which I have) and arrows to the interior of the terminal block indicating "Conventional."

Customer replied1587 days and 10 hours ago.

Hold it - I found some designations on the Chornotherm. The light is poor - I will be back in a minute with corrections

Picture
Expert:  Mark Henley replied1587 days and 10 hours ago.

Hi,

 

I'm going to hand it off to another expert as I am short on time.

 

 

Thank you,

 

Mark.

Customer replied1587 days and 10 hours ago.

Does this mean I pay again?

Picture
Expert:  Mark Henley replied1587 days and 10 hours ago.

No,

 

Not at all,

 

You haven't actually paid until you hit the accept button. Once you are satisfied with the answer.

 

Thanks

 

Mark.

Customer replied1587 days and 10 hours ago.

Okay - Should I wait until the next expert come on?

 

Picture
Expert:  Mark Henley replied1587 days and 10 hours ago.

Yes, will be just a couple minutes.

Picture
Expert:  Mark Henley replied1587 days and 10 hours ago.

Hi,

 

Go ahead and post the terminal designations, he will need them.

 

 

 

Thanks,

Picture
Expert:  Kenton Guidry replied1587 days and 10 hours ago.

Hi, I think that I can help you. can you please tell me the wire colors you were using originally?

 

Typically you will use the following.

R - Red wire - 24v power

C - - 24v common/ground

Y- Yellow wire - First stage cooling

W - White wire - First stage heating

G - Green wire - Indoor fan

O/B - - Solenoid valve

Picture
Expert:  Kenton Guidry replied1587 days and 9 hours ago.

I found the following on the Honeywell website, page 3. The link for the manual is http://customer.honeywell.com/TechLit/pdf/PackedLit/69-1896ES.pdf

 

 

 

Heat Pump Terminal Letters:

R Heating power. Connect to secondary side of heating system transformer.

Rc Cooling power. Connect to secondary side of cooling system transformer.

C Common wire from secondary side of cooling system transformer.

Y 1st stage compressor contactor.

Y2 2nd stage compressor contactor.

Aux Auxiliary heat relay.

G Fan relay.

E Emergency heat relay.

L Heat pump reset (powered continuously when System is set to Em Heat; system monitor when set to Heat, Cool or Off).

O/B Changeover valve for heat pumps.

S1 Optional outdoor or remote sensor.

S2 Optional outdoor or remote sensor.

Customer replied1587 days and 9 hours ago.

Okay - I took another look at the Chronotherm III and here is what I found

 

R Terminal - Red wire

B Terminal - Blue wire

Y Terminal - Yellow wire

 

E Terminal - Black wire (Black is jumper between E Terminal and W2)

 

W2 Terminal - White Wire & Black Wire (Black is jumper between E Terminal and W2)

 

G Terminal - Green wire.

 

On the TH8000 there is a jumber between RC and R - the manual says "Remove factory installed jumper ONLY for two-transformer systems."

 

How do you know if you have a two-transformer system?

Customer replied1587 days and 9 hours ago.

One more

After the

W2 Terminal - White Wire & Black Wire (Black is jumper between E Terminal and W2)there is another terminal O terminal - Orange wire.

 

 

 

Picture
Expert:  Kenton Guidry replied1587 days and 9 hours ago.

You know I cannot say I have ran across very many units that have a two transformer system. There are a few ways you can tell if you have more than one transformer. One is to visibly look behind the panels. Another is to look at your wiring diagram. From your first post it doesn't look like you have a two transformer system. R

Kenton Guidry39858.0164658912

Picture
Expert:  Kenton Guidry replied1587 days and 9 hours ago.

The jumper is there because you only have one power supply coming in for both heating and cooling.

Customer replied1587 days and 9 hours ago.

Okay

 

I believe I am getting this

R terminal = Red wire

Y terminal = Yellow wire

G terminal = Green wire

O/B terminal = Orange wire

 

But what about the C terminal on the Chromotherm III with blue wire to what does that connect on the TH8000?

 

 

Accepted Answer

Picture
Expert:  Kenton Guidry replied1587 days and 8 hours ago.

C would be your common 24v wire. That would go to C as well.

Expert TypeHVAC Technician
Category: HVAC
Pos. Feedback: 98.8 %
Accepts: 962
Answered: 2/14/2009

Experience: 12 years install/service experience.

Ask this Expert a Question >
Customer replied1587 days and 7 hours ago.

I forgot to ask about the white wire. On the TH8000 there is a terminal W but it appears to be the same terminal as O/B.

 

I have a white wire and an orange wire on my old thermostat (chronothem III)

Picture
Expert:  Mark Henley replied1587 days and 7 hours ago.

Hi,

 

Connect W from the old stat to the AUX on new stat.

 

Thank you,

 

Mark.

Customer replied1587 days and 7 hours ago.

I am afraid I don't see an AUX - unless it it the S1 or S2 for interior or exterior temp

 

Picture
Expert:  Mark Henley replied1587 days and 7 hours ago.

Hi,

Do you have an E? These are usully on the left hand side.

 

 

What is the exact model of stat you have?

 

Mark

Customer replied1587 days and 7 hours ago.

No E

Picture
Expert:  Mark Henley replied1587 days and 7 hours ago.

Hi,

 

If you look on the back of the stat it will have the model number on it. I need the full model number.

 

Thanks,

 

Mark

Picture
Expert:  Mark Henley replied1587 days and 7 hours ago.

Hi

 

I think what has happened is that you have a stat that is only one heat and one cool. If that is the case , do you know if you have an electric heat bank on your furnace ?

 

Did they ask you if you had more than one satge of heat where you bought the stat ?

 

 

Thanks,

 

Mark.

Customer replied1587 days and 7 hours ago.

old one The Chronotherm III -- T8611G1103 a horizontal 1 new line 9302

 

new one The TH8000 series - TH8110U002

Customer replied1587 days and 7 hours ago.

electric heat bank on your furnace? How would I know?

 

Did they ask you if you had more than one satge of heat where you bought the stat? I bought it on line - it said it would work, and since I was replacing a honeywell with a honeywell I thought it would be alright.

Picture
Expert:  Mark Henley replied1587 days and 7 hours ago.

Hi,

 

That's what I was afraid of. That is a one stage heat and one stage cool stat. That means there is no means of turning on your auxillary heating. If you know for sure that you have electric heat banks in your air handler you won't be able to use this thermostat. If you don't then you don't need the white wire.

 

To stick with the Honeywell you need a two stage heat and one cool stat, this model number will do it.

 

TH8320 or TH8321,

 

 

There are others also but these are in the same series as the one you have.

 

Thanks,

 

Mark.

Picture
Expert:  Mark Henley replied1587 days and 6 hours ago.

Hi,

 

Unfortunately they didn't ask you enough questions about your system when ordering the stat.

 

More than likely you do have at least one bank of electric heat. The easiest way to check is to open the front panel of the unit and look for some thicker wires that will be connected to some heating element terminals.

 

Thanks,

 

Mark.

Customer replied1587 days and 6 hours ago.

I know that when the AC is running in the summer the unit (it is a TRANE) outside the house runs as well as the air handler in the house. The same is true when in the winter the unit outside runs and the air handler on the inside runs. What would that mean?

Picture
Expert:  Mark Henley replied1587 days and 6 hours ago.

Hi,

 

You may not know when the electric heat bank is coming on but basically the first time of the year that it fires up you will get a burning dust smell , do you ever get that ?

 

Thanks

 

Mark.

Customer replied1587 days and 6 hours ago.

No smell.

Picture
Expert:  Mark Henley replied1587 days and 6 hours ago.

Hi,

 

The there is a possibility that you don't have auxillary heat. What climate are you in ?

 

Thanks

 

Mark.

Customer replied1587 days and 6 hours ago.

Pensacola - North West Florida. Maybe once or twice a winter it will get below 30 degrees. Rarely ever get to 25 or lower.

Picture
Expert:  Mark Henley replied1587 days and 6 hours ago.

Hi,

 

Well you could make a plan that you will just cap off the white wire and let it go until the next time you have a service done on your system and then ask the tech how many banks of heat you have. I still think you are going to have one stage of it but it may have only been used for an emergency heat back up and dedicated as just an auxillary.

 

Thank you,

 

Mark

Customer replied1587 days and 5 hours ago.

Okay

Customer replied1587 days and 5 hours ago.

On the old Stat

E Terminal - Black wire (Black is jumper between E Terminal and W2)

W2 Terminal - White Wire & Black Wire (Black is jumper between E Terminal and W2)

 

On the new one there is not E or W2 - however on the back of the stat control unit the circurit board does have printed on the board an E and a W2 - Aux. But there is no pin that would fit into the wall mount.

 

I will wait until I have the unit checked.

Picture
Expert:  Mark Henley replied1587 days and 5 hours ago.

Hi,

 

Yes , they use the same base board for all the thermostats in that series. The amount of stages needed only causes them to change the front of it. I guess it's more profitable for them that way.

 

And on the flip side of that , most heat pumps get the aux and emergency wires ran from the stat to their air handler whether they actually have them or not. So you may still not have them. We'll have to wait until we get a set of eyes on them.

 

Thanks

 

Mark.

 

 

 
Tweet

2 HVAC Technicians are Online Right Now

Ask Your Question Now
Hvac Questions Date Submitted
I have a Carrier HVAC system. Tech2000 SS. Last night it quit 6/12/2013
My son just moved in today to a house in Georgia where it is 6/11/2013
I've struggled with McQuay Enfinity Water Source Heat Pumps 6/2/2013
Bryant HVAC units, one for downstairs doesn't blow cold air, 5/31/2013
Turn on A/C without memory card? 5/28/2013
My white rogers thermostat type # XXXXX is flashing HVAC 5/20/2013
I have a Trane HVAC 5/19/2013
Hello, I have an existing Copeland Compressor for my HVAC system, 5/16/2013
I am a service tech with 49 yrs. experience in all genre of 5/15/2013
We have a Carrier 376BAW060115 model furnace. We have not used 5/12/2013
RSS
Next 10 >
Ask A HVAC Technician
Type Your HVAC Question Here...
characters left:

Top HVAC Experts

See More HVAC Technicians

In The News

Nbc
Washington Post
New York Times
Cnn
Learn More

How It Works

  • Ask an Expert
  • Get a Professional Answer
  • Ask Followup Questions
  • 100% Satisfaction Guarantee
Learn More
 
 
 

Recent Articles in HVAC

  • Electric Boiler Problems
  • Radiant Heating Problems
  • Questions on Furnace Problems
  • Air Conditioner Questions
  • Questions about Expansion Tank Problems
  • Questions about Thermocouple Problems
  • Questions about Radiator Problems
  • Air Filter Problems
  • Dehumidifier Problems
All HVAC Articles
 
 
 

Ask a HVAC Technician

Get a Professional Answer. 100% Satisfaction Guaranteed.
83 HVAC Technicians are Online Now
Type Your HVAC Question Here...
characters left:
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.
Truste
Contact Us | Terms of Service | Privacy & Security | About Us | Our Network
© 2003-2013 JustAnswer LLC
  • Pearl.com
  • JustAnswer UK
  • JustAnswer Germany
  • JustAnswer Spanish
  • JustAnswer Japan