My Coleman Evcon gas furnace kicks on for about a minute and

Customer Question

My Coleman Evcon gas furnace kicks on for about a minute and then kicks back off. I can see the pilot "element" heat up, then the gas fires up, however the gas shuts off after about 15 seconds. Thank you in advance.
Submitted: 5 years ago.
Category: HVAC
Expert:  Kenton Guidry replied 5 years ago.
Hello, my name is XXXXX XXXXX I believe I can help you. I have seen this type of problem happen before and it ended up being the pressure switch for the induce draft fan. Would you be able to jump the pressure switch?
Customer: replied 5 years ago.
Hello Kenton. I am willing to try, though I do not know how to proceed. Where is the pressure switch located and how do I jump it?
Expert:  Kenton Guidry replied 5 years ago.
The pressure switch will have a tube attached to it which runs from the pressure switch to combustion fan. it should also have two wires running to it. How familure are you with electricity?
Expert:  Rick or Nick in Texas replied 5 years ago.
HI! Sounds like the flame sensor may be dirty and needs to be cleaned. If it was anything prior in the heating sequence like the draft motor or the pressure proving switch you would not be getting ignition at all. To clean the sensor(its the wire looking thing with one wire attached to it in front of the end burner flame opposite the ignition module) remove it and clean/brighten it up with scotchbrite or fine sandpaper then reinstall it and retry it. Let me know how that works.
Expert:  Kenton Guidry replied 5 years ago.
A flame sensor would trip the unit faster than the 15 seconds it is running
Customer: replied 5 years ago.

I do not know if my previous post was posted, so here goes again.

 

I believe that I have found the pressure switch. I am somewhat familiar with electricity.

Expert:  Kenton Guidry replied 5 years ago.
You also may try accessing the ignition control to see if you have any led indications. There are only so many things that can do what is happening to your unit. If you had a meter to test for an open or closed circuit you would be able to find your problem easier.
Customer: replied 5 years ago.

Kenton:

How do I jump the switch?

Expert:  Kenton Guidry replied 5 years ago.
by touching the wires together. be careful not to hurt yourself. if this is the problem the unit should stay on.
Customer: replied 5 years ago.
There are two wires which both have a flat, slide-on attachment at the end. I removed those two wires and touched them together. Nothing seemed to happen. I did not see a spark, hear a noise or otherwise observe a change. Did I do something incorrect?
Expert:  Kenton Guidry replied 5 years ago.

I normally use a jumper wire between them so that I can reset the unit and fire it off again. You would not see a spark. Do you own an electrical meter?

Expert:  Kenton Guidry replied 5 years ago.
If you own a meter. You can test each saftey circuit to see which one is open. Also if you can access the ignition control, they sometimes have a blinking light with a code that can be looked up.
Customer: replied 5 years ago.

I don't know if this is relevant, but we received about a foot of snow last night.

 

In regards XXXXX XXXXX post about an LED indicator, there is a small silver box above the pressure switch. There is a small window through which I can see a small green LED that is solid. On the top of this box is a diagram for wiring. On the diagram it gives an indication as to diagnostic codes, flashes and fault conditions. If I am reading this correctly and the small green LED is the corresponding indicator, the system shows normal.

 

Above that area is another box, this one tan, that says Deluxe Blend Air II. It has two switches, one for Alarm and the other for Fresh Air. I believe it is for Central Air Conditioning, which we have never used. The Alarm switch is in the off position and the Fresh Air is in the on position. There are three small LED indicators on this box as well. A yellow one on the bottom (off unless I turn the Alarm swich on, which also begins a beeping sound), a green one (on and solid) and a red one on top (flashing). There is a warning that if the alarm is sounding and the red light is flashing there is a problem with the attic fan and to call for service.

 

Does any of this help?

Customer: replied 5 years ago.
Sorry didn't see your post until after I sent the most recent. Where are the safety circuits? I have an ohm meter I believe.
Customer: replied 5 years ago.

I have a multi-meter.

Expert:  Kenton Guidry replied 5 years ago.

I found an article on the Delux Blend Air at this link.

http://www.mobilehomerepair.com/ArticleBlendAir.html

I am reading throught it now to see if I can find any helpfull info.

Customer: replied 5 years ago.
Thank you.
Expert:  Kenton Guidry replied 5 years ago.

* On the Deluxe Control Box, a lit XXXXX XXXXXght indicates that the damper is open.
* A lit green light indicates that the attic fan is running.
* A flashing red light indicates that the attic fan is not running.

 

According to this information, can you tell me which lights are on.

Expert:  Josh replied 5 years ago.
HeyCustomer Is your blower motor ever kicking on after the burners fire?? The burners will fire for about 15-20 seconds to warm the heat exchanger before the limit switch brings the fan on, so you will not be blowing cold air into your house while you are calling for heat. if for some reason your fan is not coming on, (defective capacitor, defective motor, defective circuit board, defective limit switch) this would definately be the best answer to the description of your problem. kenton is correct about the flame sensor. it would shut the gas off way before 15 seconds if that was the problem. but Rick is also right in the fact that you would never get ignition if the pressure switch was the problem. these furnaces have a sequence of operations they have to go through and the presssure switch has to be proven beofre the gas valve is ever allowed to open. your problem seems to be with the blower motor or the high limit or the draft limit. not trying to say the other experts are wrong, but i feel you are checking things that arent the source of your problem.
Customer: replied 5 years ago.

Kenton:

After switching the alarm switch on, I have a flashing red, a solid green and a solid amber.

Customer: replied 5 years ago.
The blower motor is engaging both before the "fire" and continuing until after the "fire" is out.
Expert:  Kenton Guidry replied 5 years ago.

Can you use your meter and test your pressure switch, high temperature limit for a closed circuit?

Kenton Guidry, HVAC Technician
Category: HVAC
Satisfied Customers: 966
Experience: 12 years install/service experience.
Kenton Guidry and other HVAC Specialists are ready to help you
Customer: replied 5 years ago.
Sorry for my ignorance, but how do I test for a closed circuit using the meter?
Expert:  Kenton Guidry replied 5 years ago.
Customer I am sorry I wish I were more help. I am going to opt out so someone can jump in and get you taken care of. You normally put the meter on ohms and put a lead on each side of the sensor. My meter makes noise when I have a closed connection.
Customer: replied 5 years ago.

Kenton:

Thank you for your help, I really appreciate it. Sorry for being so dense!

Expert:  Josh replied 5 years ago.
so you said your blower motor is running after the burners fire??
Expert:  Josh replied 5 years ago.
r u there??
Customer: replied 5 years ago.

Hello Josh.

No, I was mistaken. It appears that as soon as the blower kicks on, the fire goes out.

 

If I tested for a closed circuit correctly, I did not hear a noise and there was not anything on the display either.

Customer: replied 5 years ago.

Sorry, I was watching and waiting on the furnace.

 

While the blower was running, the element came back on, though directly before the burners fired, the blower turned off. The burners were on for about 30 seconds, though as soon as the blower came on, the burners went off.

Expert:  Josh replied 5 years ago.
just want to verify that the blower motor is the blower in the bottom of the furnace. the inducer motor is at the top of the furnace by the vent. let's unplug the furnace and start all over. unplug the furnace, wait 5 to 10 seconds and then plug it back in, make the thermostat cal for heat and tell me exactly what happens.
Expert:  Rick or Nick in Texas replied 5 years ago.
HI! Sorry it seems like all the newbies are jumping in on our question they shouldnt be doing that and I apologize for them. I just didnt want to be rude too and really confuse you with what they are also saying so let me know who you would like to finish helping you Kent opted out for me to continue but illleave it up to you. Good luck.
Customer: replied 5 years ago.

Okay. Please stand by.

Customer: replied 5 years ago.
Sorry, it seems that everytime I post, I have to send it twice.
Customer: replied 5 years ago.

When I turned it off and then turned it back on, I increased the temperature on the thermostat. That turned on something towards the middle (I believe it may have been the inducer motor that you refered to). THen the element comes on. About 20 seconds later, the burners ignite. About 25 seconds after that, the blower comes on (it is at the top, in a silver cylindrical shaped piece of metal with "rotation" and an up-arrow stamped on it). As soon as the blower comes on, the fire goes out. After about 45 seconds, the element came on again. The burners fired and this time the blower continued, as well as the burners. The burners went off about 20 seconds later and the blower stopped after a total of about 2 minutes. About 2 minutes later, the blower came back on, though I did not see either the element or the burners light. The blower shut off after another couple of minutes.

Customer: replied 5 years ago.
Josh, are you still here?
Expert:  Josh replied 5 years ago.

i think you have a defective limit or a defective circuit board. sorry about the arguement between experts!! we are all qualified to be here or we would'nt be. it isn't professional to call other experts newbies in front of customers because they have less expericence than you. hope i helped you.

Customer: replied 5 years ago.

Sounds like I need to call a local service person to fix it then.

 

I understand with it being a public forum that there will be disagreements.

 

Thank you for your help.

JustAnswer in the News:

 
 
 
Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.
 
 
 

What Customers are Saying:

 
 
 
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
< Last | Next >
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
  • Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help. Mary C. Freshfield, Liverpool, UK
  • This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!! Alex Los Angeles, CA
  • Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult. GP Hesperia, CA
  • I couldn't be more satisfied! This is the site I will always come to when I need a second opinion. Justin Kernersville, NC
  • Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around. Esther Woodstock, NY
  • Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know. Robin Elkton, Maryland
 
 
 

Meet The Experts:

 
 
 
  • gotoman for ac

    HVAC Technician

    Satisfied Customers:

    4657
    51 years of experience install design and repair of all makes and models of AC
< Last | Next >
  • http://ww2.justanswer.com/uploads/SE/ServiceTechRus/2012-6-7_2119_056.64x64.JPG gotoman for ac's Avatar

    gotoman for ac

    HVAC Technician

    Satisfied Customers:

    4657
    51 years of experience install design and repair of all makes and models of AC
  • http://ww2.justanswer.com/uploads/AL/alumalite/2012-5-10_234018_shutterstock506249951forJA500.64x64.jpg Phil's Avatar

    Phil

    Mechanical Engineer

    Satisfied Customers:

    3888
    Retired HVAC/ Electrical & Boiler contractor. Industrial
  • http://ww2.justanswer.com/uploads/skibum0101/2008-12-16_015819_just_answer.jpg Rick Mather's Avatar

    Rick Mather

    HVAC Technician

    Satisfied Customers:

    3132
    35 years experience, HVAC
  • http://ww2.justanswer.com/uploads/RY/Rygis20/2011-5-7_3143_DSC5324.64x64.JPG Matthew's Avatar

    Matthew

    HVAC Technician

    Satisfied Customers:

    1994
    14 years experience in the HVAC field of service, installation, Manual J & D calculations
  • http://ww2.justanswer.com/uploads/KE/kentguidry/2011-9-26_214316_0059.64x64.jpg Kenton Guidry's Avatar

    Kenton Guidry

    HVAC Technician

    Satisfied Customers:

    962
    12 years install/service experience.
  • http://ww2.justanswer.com/uploads/solarman1947/2009-12-13_223915_phpkKBcXq_c2PM.jpg Rick Ridley's Avatar

    Rick Ridley

    UK Heating Engineer

    Satisfied Customers:

    871
    Retired But have had 30 years on the tools, Ex CORGI
  • http://ww2.justanswer.com/uploads/Ironheadfan/2009-12-18_222416_pump_005.jpg Tom's Avatar

    Tom

    HVAC Technician

    Satisfied Customers:

    770
    16+yrs HVAC/R service. Residential Commerical Industrial
 
 
 
Chat Now With A HVAC Technician
Kenton Guidry
Kenton Guidry
Operations Supervisor
963 Satisfied Customers
12 years install/service experience.