Why would my rheem furnace shut off before reaching the target

 

Customer Question

Why would my rheem furnace shut off before reaching the target temp, then immediately start a new heat cycle? I've jumped the 2 switches for gas flame and heat exchanger temp - no change, I've replaced the fan limit switch - no change. But, with the door off the furnace, and the safety switch taped down, the furnace will run until the target temp is reached.

Submitted: 1577 days and 19 hours ago.
Category: HVAC
Value: $15
Status: CLOSED
Picture
Expert:  Electrifier replied 1577 days and 14 hours ago.

What does taking the door off the Furnace change regarding the availibility of air to move thru the furnace? Does it open up an air flow differently than when it is installed?

Customer replied 1577 days and 7 hours ago.

There is defenitly more air with the door off. I've tried taking out the filters and letting the furnace run - door on, will still shut off before the target temp. The ducting has never been changed since installed. I bought the house the way it is. Is there anything i could check, like temp at a sensor or voltage at the board?

Picture
Expert:  Al replied 1577 days and 7 hours ago.

What kind of thermostat do you have? I believe your problem is with a setting within your thermostat. It is called a heat anticipator. If it set properly this will most likely fix your problem.

Picture
Expert:  Electrifier replied 1577 days and 6 hours ago.

What provisions do you have for combustion air in this furnace? What is the efficiency rating of the furnace?

Customer replied 1577 days and 6 hours ago.

I have a digital t stat - I replaced it 3 weeks ago. Same problem now and before. I don't think it has a heat anticipator. I can't remember the efficiency rating, but i do know that the sticker on the front read towards the lower end of the scale. Something like 83.3% sound right.

I hooker up the wires to the t stat from the instructions and it matched the old t stat. Is it possible to have the wires wrong. Can i jump two wires to eliminate the t stat as a problem?

Picture
Expert:  Electrifier replied 1577 days and 6 hours ago.

It has NOTHING to do with the thermostat. It has to do with air. When you remove the front panel you open up the furnace to receive more combustion air. When you put the panel back on you restrict this air. Without enough combustion air it won't run correctly. Check out the manufacture's installation instructions in the book provided with the furnace and read about the combustion air. Not being able to look at the furnace I can't tell you where your problem lies exactly. Is there filter material in the door? Is there an opening for combustion air? Something is restricting this air flow.

Picture
Expert:  Al replied 1577 days and 6 hours ago.

What is the brand and the model of your new digital thermostat. I can get the manual on it and tell you how to check the anticipator setting.

Customer replied 1577 days and 6 hours ago.

It is a rite temp - I bought from Home Depot. Its either MN# XXXXX or 6022. I don't have it right in front of me. I hope this helps.

Picture
Expert:  Al replied 1577 days and 5 hours ago.

Look in your manual and look under swing andthen look under calibration. Do what it says and let me know what reading you get

Customer replied 1577 days and 5 hours ago.

I'm at work right now - I can check and get back to you later tonight

Picture
Expert:  Al replied 1577 days and 5 hours ago.

That will be fine. I have a dinner appointment with a customer tonight so it will be around 9 or 10 pm CST before I can get back with you unless you post between 5 and 5 pm

 

have a good day

Customer replied 1576 days and 21 hours ago.

I checked the swing - .5

I changed it to 1.0, same result. I'm going to try removing the Air Filter again to see if the furnace will run withou anything in he duct for restriction.

Picture
Expert:  Al replied 1576 days and 11 hours ago.

Good Morning,

Check the temperature rise across the furnace. Put a thermometer in the return duct and take a reading, then put the same thermometer in the supply duct and take a reading. Subtract the return reading from the supply reading and you get the rise across the furnace. The rise should be between 30 to 70 degrees. Tell me what the rise is.

Also, check the calibration of the thermostat in your manual. Do you see a box on the back wall of the compartment where the gas valve and burners are. If you do, unplug the furnace and take the cover off. You will see a round dial face. There are 3 setpoints on that dial, the first one is "fan off", the second is "fan on", the third is "high limit". Tell me what each setpoint is.

Picture
Expert:  Electrifier replied 1573 days and 15 hours ago.

Customer

Tell me about the door you remove to make the furnace run correctly and not shut down. Is this the door on the front of the furnace where the controls are located?

Customer replied 1570 days and 19 hours ago.

I measured the temp rise across the furnace with and without the door.

With the door off intake air is 74 - 76 deg. The door outside in the garage is off and temp out there is 34 - 35 deg. The return duct is 115 - 117 deg. The furnace runs until temp is reached.

With the furnace door on, intake air is 74 - 76 deg. There is very little air coming in from the garage. The return duct is between 144 - 146 deg. The furnace has to stop and restart several times to get to target temp.

Could the furnace be overheating?

Just to be sure, I removed the air filer before measuring and testing again. The furnace can't get anymore air than its getting now.

Customer replied 1570 days and 19 hours ago.

The door for the furnace is above the burner where he blown motor is. The control board is there and a solenoid and capacitor. I think thats right.

Picture
Expert:  Electrifier replied 1570 days and 17 hours ago.

When you remove the door you allow enough air to go thru the furnace so you don't open the high limit when you have your 115 degree temp. With the door on the air flow is reduced and the air temp goes to 144 degrees. Like I said a week ago you have an air flow problem somewhere. You have some type of restriction in the return air duct preventing it from allowing the air to flow freely. Check all of your return air ducts and registers to make sure none of them are blocked. Make sure no furniture is blocking any return air register. Someplace you will find something simple I'm sure. Let me know when you find the answer.

Customer replied 1568 days and 17 hours ago.

I couldn't find any return registers blocked. I don't know if this helps, but a register that was installed into a utility room after the original furnace install. I removed it because it was attached to the garage and did not have intake air to the furnace. Is it possible that the gas valve was calibrated differently for the added air register?

I adjusted the gas pressure into the gas valve - down haft a turn. Tested the system by installed doors and running the furnace to a target temp of 3 deg. Target temp was reached and furnace did not shut off until that point.

Does this sound right to u?

Picture
Expert:  Electrifier replied 1568 days and 17 hours ago.

The gas valve shouldn't have anything to do with the amount of air circulating thru the ducts. Did you eliminate ventilation air to the return air? This is air from outside that dilutes the recirculated air with fresh air from outside? It is possible that this furnace moves much more air than the previous furnace and there is too much restriction in the return air. The key is air moving thru the furnace. Not enough air moving thru will trip the hi temp limit as you have been doing.

Customer replied 1568 days and 17 hours ago.

I checked the air supply tube from the ceiling to the top of the furnace - all clear. Checked the air conditioning coils down to the main outlet tube - all clear. All regisers clear and all have about the same air - a liittle less to the far register. Now the vent temp is 15 deg cooler than before I adjused the gas valve.

Picture
Expert:  Al replied 1568 days and 14 hours ago.

Hi! I am Al. I apologize for the confusion that you have experienced on JA. I have 35.5 years of experience in the HVAC field. I guarantee you that I can give you a solution to the problem that you are experiencing. However, I can understand how difficult it must be to differentiate the correct advise when one of JA experts is interrupting in between yours and I (AL) , communication.

I will check with my tech support team once I have your equipment information. Beware of anyone that post another answer or question concerning your issue. I will do my best to serve you with the most equitable solution to your problem. Your satisfaction is the main goal here. Give me a chance and I will provide you with a quality solution

 

To remedy the confusion you have had to deal with I will continue to work with you until you and i achieve a solution to your problem and I will do it for free. Your satisfaction is my goal. If you come to JA an experience unprofessional activity I will guarantee you a solution for free.

 

With all due respect, the electrifier is a mechanical inspector. I am a professional HVAC service technician with 35 years of technical troubleshooting experience. At this point to assure that you get a correct solution I will work with you until this issue is resolved for free. I want your problem to have a solution without you having to deal with confrontational issues from within the JA experts. So rest at ease. I guarantee you a solution with no charge. You can email me at xxxxxxxx if need be. YOUR SATISFACTION IS THE GOAL.

Gina-Mod39801.7074243866

 
Tweet

4 HVAC Technicians are Online Right Now

Ask Your Question Now
Hvac Questions Date Submitted
I have a GH19P4/5-125 Lennox furnace. My HVAC man removed 3/27/2013
Hi there, I have had a few problems with my furnace, but the 3/27/2013
Whats the rule of thumb for cost estimating a new construction 3/27/2013
Please comment on this: None of the contractors have mentioned 3/26/2013
Our school has a Weil-McLain Ultra Gas Series 3 with an outdoor 3/26/2013
I have a ge Az61ho9dabw1 heat pump and I'm trying to interphase 3/25/2013
Do you have a contract that would fairly and abundantly represent 3/25/2013
I have a Carrier electric HVAC model fk4cnb006 with variable-speed 3/23/2013
My GDH809004BXAB gas furnace stopped working 3/23/2013
RA-RP 3/23/2013
RSS
Next 10 >
Ask A HVAC Technician
Type Your HVAC Question Here...
characters left:

Top HVAC Experts

See More HVAC Technicians

In The News

Nbc
Washington Post
New York Times
Cnn
Learn More

How It Works

  • Ask an Expert
  • Get a Professional Answer
  • Ask Followup Questions
  • 100% Satisfaction Guarantee
Learn More
 
 
 

Recent Articles in HVAC

  • Electric Boiler Problems
  • Radiant Heating Problems
  • Questions on Furnace Problems
  • Air Conditioner Questions
  • Questions about Expansion Tank Problems
  • Questions about Thermocouple Problems
  • Questions about Radiator Problems
  • Air Filter Problems
  • Dehumidifier Problems
All HVAC Articles
 
 
 
close
Find Expert answers related to your question.
Sign up using email
We will never post anything without your permission.
Already have an account? Sign in

Ask a HVAC Technician

Get a Professional Answer. 100% Satisfaction Guaranteed.
4 HVAC Technicians are Online Now
Type Your HVAC Question Here...
characters left:
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.
Truste
Contact Us | Terms of Service | Privacy & Security | About Us
© 2003-2013 JustAnswer LLC