I need the wiring diagram hobart lxih dishwasher 120/208-240

Customer Question

I need the wiring diagram for a hobart lxih dishwasher 120/208-240 3w does the 3w need 2 50 amp breakers or 3?
Submitted: 12 months ago.
Category: Electrical
Expert:  ProGrade replied 12 months ago.
Welcome to www.justanswer.com
This unit requires 3 hots on a 50A 3-pole breaker and one ground wire. It does not require 2 or 3 circuits, only one 3-phase circuit. Unless distance to the panel is excess, 3 each #6 Copper plus a # ***** Copper ground.
Expert:  ProGrade replied 12 months ago.
One 50 Amp 3-phase circuit. Let me know if you have any other questions. Thank you
Customer: replied 12 months ago.
That is how I have it wired now. I would like to see the diagram to confirm since what the manual states is*The (3W) systems require three power wires that include a current carrying neutral. An additional
fourth wire must be provided for machine ground.
Expert:  ProGrade replied 12 months ago.

That is correct & i stand corrected on the circuit/breaker. The circuit should consist of 3 ea - #6 copper (2 hots & 1 neutral) plus 1 ea - #8 ground wire for a total of 4 conductors on a 2-Pole 50 Amp Breaker.

There is no wiring diagram in the manual.

Here is a link to the manual if you do not have it:

https://www.google.com/url?sa=t&source=web&rct=j&url=http://www.whaleyfoodservice.com/EquipmentManualsIntegration/Manuals/HOB1313.pdf&ved=0ahUKEwiPx5eDk9HNAhVIXR4KHagaAAwQFggbMAA&usg=AFQjCNGWI-r_hU_1AS782OcEGSFLGaYV2Q&sig2=RkBcFcjY0Gbr3KQ9YIRAQQ

Expert:  ProGrade replied 12 months ago.

Is the neutral wire identified in the junction box on the unit? If so, one hot to each of the load conductors, the neutral to neutral & the # ***** to ground.

Customer: replied 12 months ago.
I have the manual which is why I started this question to see the wiring diagram. If I had gone with your
first answer which is what I assumed until I found the manual I may have been wrong. Without a definitive of the wiring diagram I do not feel like I should have to pay for this answer. Are you positive 2 pole 50 amp breaker plus neutral and
4th wire ground.
Expert:  ProGrade replied 12 months ago.
I am certain that is what the manual indicates. Thanks
Expert:  ProGrade replied 11 months ago.
how did it work?
We are on the honor system here. If you don't rate my service, I am working for free. I would appreciate a positive rating. Thank you