I have a strange problem I need help with. I have a wall outlet

Resolved Question:

I have a strange problem I need help with. I have a wall outlet that tests an open negative. The strange thing is the outlet is wired on the lower end of the outlet with correct wiring. The top portion of the same receptacle has no wiring attached and reads the open neutral. The outlets to either side of the improper outlet are wired correctly and the garage is powered from a 90 amp circuit from the main panel fed with 2 30 amp fuses. The garage is divided into 2 circuits. Any advice you could provide would be greatly appreciated.
Submitted: 1 year ago.
Category: Electrical
Expert:  Mike G. replied 1 year ago.
Hi, I'm Mike and I'll be glad to assist you. There must be an outlet or junction ahead of the problem. A quick way to know is to short the circuit hot to ground. This will kill the circuit and you will then see what is ahead of the problem.
Customer: replied 1 year ago.


how do I short the hot to the ground?? Black wire to grounding screw??

Expert:  Mike G. replied 1 year ago.
Try this procedure first.

Wiggle Procedure

You have a circuit with dead outlets and maybe some dead lights on it or you’re experiencing flickering on a circuit. You will need a 2 wire voltage tester to check the outlet. A Multimeter or a Volt/Con are suggested. I prefer the Volt/Con because there are no settings to make, it does continuity and is audible. Success begins with knowing what you’re looking for.

1] No voltage reading between the hot and the neutral or ground indicates an open hot.

2] No reading between the hot and the neutral but 120V between the hot and ground and 120V between the neutral and ground indicates an open neutral.

3] No continuity between the neutral and ground – Check for tripped GFCI device first

4] If all the branch circuit breaker are on you have a bad connection on the hot or neutral wires. The usual cause is a bad connection, either a termination on a device or connection in a wire nut.

Over the years I’ve found the easiest way to locate the opening needing examination and correction is to wiggle the devices.

5] The first step in this exercise is to get a lamp to act as an alert. Make sure the lamp works and in the on position. You may also use something like a vacuum cleaner or blow dryer, for an audible alert. Don’t use anything electronic, like a radio.

6] Plug it into a dead outlet.

7] Now with a cube tester or any plug you will need to go to all the dead outlets and any live outlets in the area, insert the plug and wiggle the device side to side slightly. Watch the test lamp or listen for the other alerts as you wiggle the devices.

If the loose or bad connection is present the wiggle action may make it contact briefly and the lamp or the other things will alert you . Having found the suspected outlet all that is left is to correct the bad connection.

If the device is a push back wired device, this probably is the cause of the circuit failure. All wires must be terminated under the screws. Also you should never put more than one wire under a screw.

This troubleshooting procedure works in most cases and won’t have you open boxes un-necessarily. Keep in mind that the problem is in one of two places in the circuit, either in the first dead outlet or the live outlet just ahead of it.

Customer: replied 1 year ago.


thanks so much I did try the wiggle method as you described and nothing on the light "flickered" even detached the receptacle from junction box and tried again with no disruption and still open neutral. The receptacle directly in front has adequate wiring with correct indicator lights on hand held tester. Can there be 2 grounding wires attached to the grounding screw on one outlet. I did disconnect the two grounding wires and reattached with one only and still open neutral. I am obviously not an electrician but this one is frustrating

Expert:  Mike G. replied 1 year ago.
There being 2 ground would say that one is supply side and the other is to the down strean outlets.
Customer: replied 1 year ago.


sorry to keep bothering you LOL. The two ground wires were created from running an additional outlet above the original outlet. Only one portion of the original outlet was wired so I ran a new wire from the top portion of the original outlet to a new outlet above the original. When the open neutral occurred I completely detached the new outlet wiring and still have open neutral. Frustrating as can be

Expert:  Mike G. replied 1 year ago.
No bother. If the procedure didn't work only means that the neutral wire isn't close enough to make contact with a wiggle or it is open in a light fixture opening or junction box. Either flash the circuit as I originally told you or install a tempory jumper between the neutral and ground. This would make the outlet live and when the circuit is turned off at the breaker you will see if other outlet go dead and thus show where you need to examine for the open.
Customer: replied 1 year ago.


Will that be a stripped wire from ground to neutral and I don't have a breaker its on a 30 amp fuse

Expert:  Mike G. replied 1 year ago.
That is no doubt why you lost the neutral. The circuit being over fused cause the wire or connections to fail with an overload. The jumper from the ground to the neutral only re-establishes the circuit for testing.
Customer: replied 1 year ago.


should the fuse be replaced with a smaller amperage and what you are saying is the circuit is full and can not handle another outlet

Expert:  Mike G. replied 1 year ago.
Circuit should be fused for the wire that was used. #14 wire = 15A, #12 wire=20A. The outlets are also rated for the circuit and 30A is way over.
Customer: replied 1 year ago.


wow ok will check the wire size and replace with proper sized fuse will that restore the neutral and allow proper function. Thanks for all your help I appreciate your time and patience with me on this

Expert:  Mike G. replied 1 year ago.
You're welcome. In todays world breakers are the way to go. You might consider a panel change to avoid future problems.
Customer: replied 1 year ago.


I know I have an old Wadsworth panel and the garage is a square D fuse panel and the cost to replace these will be significant. If I replace the fuse with proper amperage will that restore safe operation.

Expert:  Mike G. replied 1 year ago.
Yes it would. They make a breaker fuse that would be better instead of a standard fuse.. That would be a better alternative.
Mike G., Master Electrician
Category: Electrical
Satisfied Customers: 5642
Experience: Proven Professional 45 years Experience
Mike G. and other Electrical Specialists are ready to help you
Customer: replied 1 year ago.


Thank you again for all your help you have been excellent

Expert:  Mike G. replied 1 year ago.
Well, thanks and good luck.

JustAnswer in the News:

 
 
 
Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.
 
 
 

What Customers are Saying:

 
 
 
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
< Last | Next >
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
  • Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help. Mary C. Freshfield, Liverpool, UK
  • This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!! Alex Los Angeles, CA
  • Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult. GP Hesperia, CA
  • I couldn't be more satisfied! This is the site I will always come to when I need a second opinion. Justin Kernersville, NC
  • Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around. Esther Woodstock, NY
  • Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know. Robin Elkton, Maryland
 
 
 

Meet The Experts:

 
 
 
  • Mike

    Master Electrician

    Satisfied Customers:

    1425
    Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer
< Last | Next >
  • http://ww2.justanswer.com/uploads/mikepettinato/2009-9-4_41145_DSC005132.jpg Mike's Avatar

    Mike

    Master Electrician

    Satisfied Customers:

    1425
    Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer
  • http://ww2.justanswer.com/uploads/WI/WireitUp/2012-6-17_18212_Photo00006.64x64.jpg Jason's Avatar

    Jason

    Service Technician

    Satisfied Customers:

    3278
    Over 15 years of experience in all types of installations, troubleshooting, and repairs.
  • http://ww2.justanswer.com/uploads/MI/MikeG2010/2012-6-7_192640_IMG01612.64x64.jpg Mike G.'s Avatar

    Mike G.

    Master Electrician

    Satisfied Customers:

    5318
    Proven Professional 45 years Experience
  • http://ww2.justanswer.com/uploads/AS/AssuredElectrical/2011-9-13_221243_me.64x64.gif AssuredElectrical's Avatar

    AssuredElectrical

    Master Electrician

    Satisfied Customers:

    2149
    Contractor-40 Years in the ElectricalTrade
  • http://ww2.justanswer.com/uploads/electrifier/2008-12-16_200429_headbob1.jpg electrifier's Avatar

    electrifier

    Master Electrician

    Satisfied Customers:

    1454
    Electrical contractor and electrical inspector for over 24 years with phone and networking expertise
  • http://ww2.justanswer.com/uploads/rich03dungo/2010-3-17_101556_tshirt2.jpg Rich's Avatar

    Rich

    Master Electrician

    Satisfied Customers:

    1115
    Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain
  • http://ww2.justanswer.com/uploads/UR/urelectrician/2012-9-28_223652_JustAnswerPic.64x64.jpg Kevin's Avatar

    Kevin

    Licensed Electrician

    Satisfied Customers:

    993
    27 years as a Licensed Electrical Contractor in Illinois, 5 year college Electrical Instructor, Former Electrical Inspector, Diploma in Digital Electronics, Former Illinois Licensed Home Inspector
 
 
 
Chat Now With An Electrician
Mike G.
Mike G.
Master Electrician
5598 Satisfied Customers
Proven Professional 45 years Experience