My house was built in 1959; no ground wires, no mental conduit.

Resolved Question:

My house was built in 1959; no ground wires, no mental conduit. I have read several of your answers on this subject and it seems that GFIs are the best solution. But from a technical point of view what is the shock hazard or other disadvantage of connecting the grounding terminal of an outlet to the white wire, it's always grounded?
Submitted: 6 months ago.
Category: Electrical
Expert:  AssuredElectrical replied 6 months ago.

AssuredElectrical :

Welcome. My name is XXXXX XXXXX would be glad to assist.

AssuredElectrical :

Ok, understand. Let me try to explain. The white wire (neutral) is the other half of 120 volts. Hot and neutral make a complete circuit. The neutral wire, actually carries the same current as the hot wire. It is the return on the AC cycle of power. So, since grounds are for short circuit and protection, if you use the white wire connection and something happens, you could actually charge the ground with voltage and it is now dangerous and not safe.

AssuredElectrical :

The GFCI on the circuit will assist for personal protection and allow changing receptacles to a 3 prong, but there is still no ground present. If a ground is wanted, the code now allows the installation of a single ground wire to attach to the receptacle.

AssuredElectrical :

Here is the writing of the code on that subject:

AssuredElectrical :

250.130
(C) Nongrounding Receptacle Replacement or Branch
Circuit Extensions. The equipment grounding conductor
of a grounding-type receptacle or a branch-circuit extension
shall be permitted to be connected to any of the following:
(1) Any accessible point on the grounding electrode system
as described in 250.50
(2) Any accessible point on the grounding electrode conductor
(3) The equipment grounding terminal bar within the enclosure
where the branch circuit for the receptacle or
branch circuit originates
(4) For grounded systems, the grounded service conductor
within the service equipment enclosure
(5) For ungrounded systems, the grounding terminal bar
within the service equipment enclosure


250.50 is the panel and ground electrodes like rod, rebar,main ground wire
to water piping etc.

AssuredElectrical :

Let me know if any other information is needed, just reply. Thanks

Customer:

--- If something happened?? like what. The white wire us still connected to ground!

AssuredElectrical : The code is specific for the exact reason to protect life. If the white becomes loose anywhere in the circuit, anything connected to that ground connection will become the path on the circuit. So, if you have a lamp lugged into that receptacle and touch the lamp, it will electrocute you and possible kill.
AssuredElectrical : Bad rating is certainly unjustified. I cannot help it if the facts and safety of the situation are not suited and are not what you were hoping.
Customer:

You did not answer my question. How can the ground terminal be hot as long as it is tied to the white wire which is tied to ground?

AssuredElectrical : I believe you fail to realize, on a normal circuit, there are 3 wires. One hot, one neutral and one ground. So they serve 3 distinct purposes. One is the power SOURCE (black wire) from the transformer from the street, one is the neutral source which RETURNS power to the transformer from the street, and One is the safety ground that is only at you panel and not coming from the street. Power flows from the hot wire, through the light or what ever is attached, then flows back to the street through the neutral. So, if you use the white to ground a receptacle. The white becomes loose anywhere on that circuit, anything attached to the ground will be the path of return. The white is NOT ENERGIZED, but is the grounded side of power necessary to operate anything on the circuit. You will become that other half and power will flow from YOU to the light, that is what electrocutes and kills.
AssuredElectrical : Do this, connect one wire to one side of a light bulb. Connect another wire to the other side. Now, connect one of those to a breaker, then connect the other one to your fingers, which is normally neutral and you will be electrocuted.
AssuredElectrical : A circuit must be completed from Hot to Neutral. Anything that gets in between them will be electrocuted. Electricity does not flow one direction.
AssuredElectrical : A neutral can kill you just like the 120 volt source from the breaker, if you are put between the circuit
AssuredElectrical :

Full Size Image

Customer:

Well Sir, a circuit could become completed from a Hot, (black wire) to a ground, (maybe the housing of a lamp, with me in between and that would be bad), but this could happen with any properly connected circuit. So why is it worse to be groundes through normal ground wire than thru a grounded white wire.

AssuredElectrical :

In a normal properly system, it cannot connect to ground because it will trip the breaker or blow the fuse.

AssuredElectrical :

Please understand, the ground at your house originates at your panel and does not come from the utility company.

Ground at the panel connects to either a ground rod outside, metal water piping that goes outside in the ground to
the street and or both on older homes.

Ground wires are totally separate throughout the house.

Yes, on older homes prior to the new codes, the neutral connects to the same bar as the ground.
But that is only at the panel and cannot even touch anywhere else on the receptacle and light circuits.

There is a separate wire for that connection when running to receptacles and lights etc. with a grounded system.

So, it is IMPOSSIBLE to create the same issue as using neutral for ground because of the
extra wire.

AssuredElectrical :

Just for clarity, the neutral is a GROUNDED CONDUCTOR and is designed to carry current (other side of power) The ground wires are not and should never be used as such.

AssuredElectrical :

I am sorry if there is some reason that you do not understand the seriousness/dangers of using the neutral
on a circuit for the grounding also.

I do believe the desription and image posted show and explain why it cannot be done (connecting to neutral
for use as a ground).
40+ years in the industry and qualified and licensed by the state to all electrical work.

If you were to connect the ground post to the neutral, you will put yourself, any friends, or family in danger of electricution.
It is extremely dangerous, illegal and will eventually hurt or kill someone.

Customer:

I think we should stop chat -- we're getting some where but not to the answer. I still think a ground to the white wire is better than no ground at all. If the GOOD rating is not good enough let me know. The chat was worth the $12. Thanks XXXXX

AssuredElectrical :

I do appreciate an upgrade to good rating.--- Unsure of how else to explain, that connecting the ground screw of a receptacle to the neutral wiring, is not grounding the receptacle, but allowing a different path for return power to get enter the system through someone or something if and when a mere loose connection in the neutral circuit happens.

Customer:

P.S. As long as we are exchanging qualifications, I have a BS degree in electrical engineering from Colorado State University, 1952. I then worked for Sandia Labs. for 40 years in electrical engineering. I think I know the subject. Russ

AssuredElectrical :

Ok, thanks. Take care Russ

AssuredElectrical, Master Electrician
Category: Electrical
Satisfied Customers: 2738
Experience: Contractor-40 Years in the ElectricalTrade
AssuredElectrical and other Electrical Specialists are ready to help you

JustAnswer in the News:

 
 
 
Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.
 
 
 

What Customers are Saying:

 
 
 
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
< Last | Next >
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
  • Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help. Mary C. Freshfield, Liverpool, UK
  • This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!! Alex Los Angeles, CA
  • Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult. GP Hesperia, CA
  • I couldn't be more satisfied! This is the site I will always come to when I need a second opinion. Justin Kernersville, NC
  • Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around. Esther Woodstock, NY
  • Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know. Robin Elkton, Maryland
 
 
 

Meet The Experts:

 
 
 
  • Mike's Avatar

    Mike

    Master Electrician

    Satisfied Customers:

    1425
    Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer
< Last | Next >
  • http://ww2.justanswer.com/uploads/mikepettinato/2009-9-4_41145_DSC005132.jpg Mike's Avatar

    Mike

    Master Electrician

    Satisfied Customers:

    1425
    Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer
  • http://ww2.justanswer.com/uploads/WI/WireitUp/2012-6-17_18212_Photo00006.64x64.jpg Jason's Avatar

    Jason

    Service Technician

    Satisfied Customers:

    3094
    Over 15 years of experience in all types of installations, troubleshooting, and repairs.
  • http://ww2.justanswer.com/uploads/MI/MikeG2010/2012-6-7_192640_IMG01612.64x64.jpg Mike G.'s Avatar

    Mike G.

    Master Electrician

    Satisfied Customers:

    4946
    Proven Professional 44 years Experience
  • http://ww2.justanswer.com/uploads/SI/sirsparks/2011-3-13_01226_VZ20092.64x64.jpg Sir Sparks's Avatar

    Sir Sparks

    President/Owner/ Master Electrician

    Satisfied Customers:

    2519
    US State Certified & UK Electrical Contractor for all electrical fields/disciplines
  • http://ww2.justanswer.com/uploads/AS/AssuredElectrical/2011-9-13_221243_me.64x64.gif AssuredElectrical's Avatar

    AssuredElectrical

    Master Electrician

    Satisfied Customers:

    1866
    Contractor-40 Years in the ElectricalTrade
  • http://ww2.justanswer.com/uploads/electrifier/2008-12-16_200429_headbob1.jpg electrifier's Avatar

    electrifier

    Master Electrician

    Satisfied Customers:

    1433
    Electrical contractor and electrical inspector for over 24 years with phone and networking expertise
  • http://ww2.justanswer.com/uploads/rich03dungo/2010-3-17_101556_tshirt2.jpg Rich's Avatar

    Rich

    Master Electrician

    Satisfied Customers:

    1114
    Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain