Grounding required for PVC box?

Resolved Question:

I sell electrical devices across the country. My devices plug into a 120V wall outlet with a rubber-jacketed cord (3x18 gage conductors) that has a 3 prong NEMA 5-15 plug. The cord feeds AC power to my device which is contained in a PVC junction box. There are no metal parts exposed on the outside of this box, or on the inside. (no mounting plates for example)  The device contains a tiny AC/DC convertor (enclosed in a smaller plastic box)  which draws something like 50mA to power an LED and piezobuzzer. Is it required by the NEC or any other regulating body for my customers connect the (currently unused) ground wire in my cord?  If so, why?  (I don't see the point)  And what would it be connected to?

Submitted: 10 months ago.
Category: Electrical
Expert:  AssuredElectrical replied 10 months ago.
Welcome. My name is XXXXX XXXXX would be glad to assist.

Can you be a little more specific on the situation?

Your cord has 3 prong plug on the end to plug into a receptacle, correct?

The question on the customer connecting the ground is referencing what exactly?

Thanks
Customer: replied 10 months ago.

Can't get my response through to you after two attempts. Please contact me at my emailXXX@XXXXXX.XXX

Expert:  AssuredElectrical replied 10 months ago.

Unfortunately there is no email communications with the site. All posting are done in this forum.

 

Is there a problem that you cannot see this posting?

 

Not sure what the communication avenue you have attempted?

 

Customer: replied 10 months ago.

I would like to change my question a bit as follows in order to get a more encompassing answer:


 


There is no 3-prong plug as I said initially, instead, I am providing my customer with a 3-conductor wire that connects to my device. The 3-conductor wire is not connected to anything in my device because there is no place to connect it to - its a PVC outlet body with no metal parts outside or inside. (except wires leading to an AC/DC convertor which is enclosed in its own plastic box within the outlet body) The 3-conductor wire is to be "hard wired" to my customer's 120VAC or 240VAC electrical source. My question is:


1) Do I have to connect the ground wire to anything in my device?


2) Must my customers they connect the ground wire at their electrical source?


Please include NEC code references.

Expert:  AssuredElectrical replied 10 months ago.

Thanks for the information.

 

As for your "device", has it been and labeled as UL approved?

 

That is the first thing that comes to mind.

 

The NEC does not nor has ever governed any piece of equipment, appliance or apparatus.

 

Equipment is approved by UL and when done so, it has already met the requirements that are associated in its UL category.

 

NEC covers wiring installations in all aspects of buildings and its surroundings.

 

No different than a light fixture or dishwasher etc. NEC has no ruling on these items.

 

They only rule on the permanent wiring of the structure to allow connection of the items

 

So, in your case, it appears there is no relation to the NEC, only UL.

 

As far as NEC on grounds, if it has metal of any type, grounding is required.

If there is no metal, then a ground cannot be established nor required.

 

But that pertains to the electrical system of the building and each part has a different article in the code.

Grounding is covered in 100+ locations as it pertains to each part of the electrical system of the building.

 

 

As an example, look at all the lamps, radios and other electrical appliances purchased. Most have no ground because of the UL approval.

They work with the appliances , not the NEC

 

Hope that helps, just reply for clarification ot other information.

Thanks

Customer: replied 10 months ago.

Thanks Tommy, this is closing in on an answer, but I am still not clear on everything.


 


You are saying that NEC does not have authority over devices such as radios, or my device - but only wiring in buildings. But then you said:


As far as NEC on grounds, if it has metal of any type, grounding is required.


My device does have copper wires internally connected to the internal AC/DC convertor which is basically a pcb with a metal-core transformer. (also found in radios) So there must be some distinction as to the nature of the metal: do you mean external metal that can be touched by a person? (although many radios have this too in the form of antennas. Maybe you mean" "electrically connected external metal that can be touched by a person"? Please clarify.


 


Also from what you have said, it seems to me that if I provide my device with a NEMA plug then that is the magic point at which the NEC has no oversight like with a radio. However my device will be hard-wired to the building's wiring through a junction box, so doesn't that make it a permanent part of the building wiring and therefore subject to the NEC code?


From your answer "But that pertains to the electrical system of the building... "


 


So, I'm still not clear on if the ground wire must be connected or not. even though it doesn't seem to serve much purpose running for the 8 ft length of the wire and then dead-ending inside my device.


 

Expert:  AssuredElectrical replied 10 months ago.

Ok, sorry for any confusion. Probably should have clarified what I was posting.

 

The NEC has no authority and does not dictate over appliances,radios, lamps etc or consumer products in general. Those fall solely under the UL.

 

I was just giving an example of what the NEC requires on equipment that is part of a structure and its wiring premises.

Like switches, receptacles, boxes etc.

 

Just for the situation, lets say that your item was actually part of a buildings wiring system.

Even if internal components have metal, it would be required to be grounded under the NEC. Any metal whether it is immediately accessible or only accessible after removing a cover is required to be grounded.

 

If there is no metal then it cannot be grounded, therefore not required.

Similar to running pvc pipe and pvc boxes with wires inside the conduit.

The boxes nor the conduit have any grounding capability because it is all plastic.

But when the wires emerge out of the pipe, if there is something with metal, then it is grounded at that point, otherwise you would not even run a ground wire.

 

But again, they do not govern as posted above.

 

If you have nothing metal inside or out, why use a 3 wire cord and plug, use a 2 wire only.

 

Hope that clarifies any confusion.

Thanks

 

 

Customer: replied 10 months ago.

Thank you Tommy, just so I am clear: you are saying that the fact that my device is hard-wired does not have any bearing at all on whether it is subject to NEC regulations, instead the important thing is if my device is considered "equipment that is part of a structure and its wiring premises." Only this equipment is governed.



Well I can say that my device is not part of a structure, however I don't know if the term "wiring premises" contains a hidden meaning that would be unknown to a lay person so here is what I think it means by example:



  • Wiring that is considered part of the building (like an illuminated EXIT sign) would fall under the NEC regulations since the sign is required to be there by other regulatory authorities and is expected to always be in place. However if an occupant of the building installed an almost identical illuminated sign that read instead "ON AIR" (for a radio broadcast booth for example) then it would not be subject to NEC regulations because the sign is not considered a permanent part of the "wiring premises" of the building?


In other words electrical devices that would be expected to serve any occupant of a building would be considered "wiring premises" but if a device has a specific purpose for only one occupant the it is not wiring premises? Is there a better definition?



If my above example is correct then my device would not be considered "wiring premises" and therefore would not be subject to any NEC regulations, and would therefore not require any grounding?


Peter XXX-XXX-XXXX

Expert:  AssuredElectrical replied 10 months ago.

Using your example:
Wiring that is considered part of the building (like an illuminated EXIT sign) would fall under the NEC regulations since the sign is required to be there by other regulatory authorities and is expected to always be in place. However if an occupant of the building installed an almost identical illuminated sign that read instead "ON AIR" (for a radio broadcast booth for example) then it would not be subject to NEC regulations because the sign is not considered a permanent part of the "wiring premises" of the building?

In your example, the sign itself is under UL, not the NEC. The sign is a consumer product.

In that case, NEC states to follow manufacturers recommendations when connecting and installing because the UL has already approved the drawings-wiring-components etc for consumer use.

The wiring from the circuit breaker to the sign is under the NEC .

The manufacture of the sign just like a table lamp, a radio,a fan, or any other consumer product and is not governed by NEC.

I am not sure how else to word it or explain.

Your item would be considered a consumer product and falls under the UL.

The receptacle and wiring you plug it into would fall under NEC.

 

Hard wired or plug connected, it is still a consumer product for UL standards and not the NEC

Customer: replied 10 months ago.

OK so now it is clear to me that NEC does not govern the installation of anything beyond my customer's junction box. But I still don't have an answer to my original question which was:



  • Is it required by the NEC or any other regulating body for my customers connect the (currently unused) ground wire in my cord


 


My device, like thousands of other industrial products with a sales volume too small to justify UL's substantial fees, is not UL approved. Is there any regulating body or government agency that requires a product to meet UL's standard? Have approval that it meets the standard from a test lab?

Expert:  AssuredElectrical replied 10 months ago.
If there are no metal parts outside or inside, the ground wire is of no value and therefore is not required and does not need to be attached.
It would be the same as a plastic fan which has only a 2 prong cord. Nothing to touch that could create a shock hazard, so grounding is not necessary or even possible. ( I have several of these myself)


The remainder was not in the original question so:
As for regulating bodies or government agency on the UL, It would be necessary to consult an attorney on those issues, as the liability exists for any potential issue that could cause harm or damage to anyone or anything.

Every municipality, city, and state will all have different laws on the books for consumer protection rights.
That does not have anything to do with the grounding, it is about the product and liability.
AssuredElectrical, Master Electrician
Category: Electrical
Satisfied Customers: 2963
Experience: Contractor-40 Years in the ElectricalTrade
AssuredElectrical and 3 other Electrical Specialists are ready to help you

JustAnswer in the News:

 
 
 
Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.
 
 
 

What Customers are Saying:

 
 
 
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
< Last | Next >
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
  • Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help. Mary C. Freshfield, Liverpool, UK
  • This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!! Alex Los Angeles, CA
  • Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult. GP Hesperia, CA
  • I couldn't be more satisfied! This is the site I will always come to when I need a second opinion. Justin Kernersville, NC
  • Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around. Esther Woodstock, NY
  • Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know. Robin Elkton, Maryland
 
 
 

Meet The Experts:

 
 
 
  • Mike

    Master Electrician

    Satisfied Customers:

    1425
    Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer
< Last | Next >
  • http://ww2.justanswer.com/uploads/mikepettinato/2009-9-4_41145_DSC005132.jpg Mike's Avatar

    Mike

    Master Electrician

    Satisfied Customers:

    1425
    Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer
  • http://ww2.justanswer.com/uploads/WI/WireitUp/2012-6-17_18212_Photo00006.64x64.jpg Jason's Avatar

    Jason

    Service Technician

    Satisfied Customers:

    3278
    Over 15 years of experience in all types of installations, troubleshooting, and repairs.
  • http://ww2.justanswer.com/uploads/MI/MikeG2010/2012-6-7_192640_IMG01612.64x64.jpg Mike G.'s Avatar

    Mike G.

    Master Electrician

    Satisfied Customers:

    5318
    Proven Professional 45 years Experience
  • http://ww2.justanswer.com/uploads/AS/AssuredElectrical/2011-9-13_221243_me.64x64.gif AssuredElectrical's Avatar

    AssuredElectrical

    Master Electrician

    Satisfied Customers:

    2149
    Contractor-40 Years in the ElectricalTrade
  • http://ww2.justanswer.com/uploads/electrifier/2008-12-16_200429_headbob1.jpg electrifier's Avatar

    electrifier

    Master Electrician

    Satisfied Customers:

    1454
    Electrical contractor and electrical inspector for over 24 years with phone and networking expertise
  • http://ww2.justanswer.com/uploads/rich03dungo/2010-3-17_101556_tshirt2.jpg Rich's Avatar

    Rich

    Master Electrician

    Satisfied Customers:

    1115
    Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain
  • http://ww2.justanswer.com/uploads/UR/urelectrician/2012-9-28_223652_JustAnswerPic.64x64.jpg Kevin's Avatar

    Kevin

    Licensed Electrician

    Satisfied Customers:

    993
    27 years as a Licensed Electrical Contractor in Illinois, 5 year college Electrical Instructor, Former Electrical Inspector, Diploma in Digital Electronics, Former Illinois Licensed Home Inspector