20KW Kohler generator install. Have about a 110 run. Plan

Resolved Question:

20KW Kohler generator install. Have about a 110' run. Plan was ~20ft burried to house, ~90' in house. 2 continuous conduit runs. (1) 3/4" for the control (Belden shielded twisted pair + CAT5e). (1) 1-1/4" for the (3) #3THHN, 2 HOT, 1 RTN (1) #6THHN (grd) and (1) UF rated 14/2 for the gen battery charger.

Questions.
With the (3) #3s and the 14/2, does that count as "more than 3" current carrying conductors, and thus require de-rating? I think that it counts for 4.

Is it permissible to have the 14/2, (3) #3s and (1) #6 in one 1-1/4" conduit for ~110'?

Is it permissible to have the 14/2 in conduit?
Submitted: 1 year ago.
Category: Electrical
Expert:  electrifier replied 1 year ago.

electrifier :

14/2 NM cable is not made to be installed in conduit. Your feeder that consists of 2 hots, a neutral and a ground is actually 2 current carrying conductors as the neutral only carries the imbalance of the 120/240 volt feeder. Your 2 conductors for the charger would count as 2 more for a total of 4 conductors. The amperage of the charger circuit is almost nothing as it is a trickle charger. A 20 Kw generator does not product 100 amps. It is actually 80 amps and #3 THHN in conduit is allowed for 110 amps in a residential installation. You are fine with the #3 for the hot conductors. This comes from the 2011 NEC and has not changed in years. Voltage drop is not an issue for 110' of feeder.

Customer:

The 14/2 is not NM, but UF, outdoor rated. I'm pretty sure that the inspector is going to want the 14ga wire in conduit for the exterior portion, does that mean that I need to go to 14g THHN wire? I'm only going to have 1 entrance for all of the power, (Kohler spec) and 1 for the LV. If I cant run the 14/2 in the conduit with the #3, what would the inspector want to see? Branch it out and re-join?

electrifier :

I can't speak for other inspectors, some have "preferences" they like to require while not supported by the code. UF is treated the same as NM cable. UF is approved for direct burial. This is simply the circuit for the battery charger and is a very low load. THHN would be the correct wire to run in the conduit. Does the generator call for #3 Copper wire? Is it a specification?

electrifier :

Is your transfer switch rated for use as service equipment? Is it the SA7 kit or the SA2 kit?

Customer:

It is the SA7 kit, so yes it is rated as a service entrance. It does not call for #3 but it has a 100A breaker...

electrifier :

Does this connect to LP or Natural Gas? This makes a difference in the amperage output and the generator rating, 20 Kw or 17 Kw. LP is 20 Kw.

Customer:

Its LP. So the nameplate has 75A, the 20KW for LP is 83.3A, and the breaker is 100A. I am using THHN-2 for both the #3 and the #14. I've pulled the 14/2 and will run 3 individual runs for the #14 (HOT,RTN &GRD). If I am correct, the 90deg column (applicable for THHN-2) rates the #3 for 110A and the #14 for 25. If I need to de-rate 20%, that pulls the #14 down to 20A, which should be fine, but the #3 down to 88A. Does that meet code?

electrifier :

This is residential. There is a table that says #4 is good for 100 amps residential and #3 is good for 110 amps. 4 - 6 current carrying conductors is derated to 80% so that is 88 amps for #3 and your capacity is 83 amps so no problem at all.

electrifier :

It should not be necessary to run a 2nd ground in the conduit, only a single #6 would be required.

electrifier, Master Electrician
Category: Electrical
Satisfied Customers: 1630
Experience: Electrical contractor and electrical inspector for over 24 years with phone and networking expertise
electrifier and other Electrical Specialists are ready to help you

JustAnswer in the News:

 
 
 
Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.
 
 
 

What Customers are Saying:

 
 
 
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
< Last | Next >
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
  • Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help. Mary C. Freshfield, Liverpool, UK
  • This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!! Alex Los Angeles, CA
  • Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult. GP Hesperia, CA
  • I couldn't be more satisfied! This is the site I will always come to when I need a second opinion. Justin Kernersville, NC
  • Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around. Esther Woodstock, NY
  • Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know. Robin Elkton, Maryland
 
 
 

Meet The Experts:

 
 
 
  • Mike

    Master Electrician

    Satisfied Customers:

    1425
    Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer
< Last | Next >
  • http://ww2.justanswer.com/uploads/mikepettinato/2009-9-4_41145_DSC005132.jpg Mike's Avatar

    Mike

    Master Electrician

    Satisfied Customers:

    1425
    Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer
  • http://ww2.justanswer.com/uploads/WI/WireitUp/2012-6-17_18212_Photo00006.64x64.jpg Jason's Avatar

    Jason

    Service Technician

    Satisfied Customers:

    3278
    Over 15 years of experience in all types of installations, troubleshooting, and repairs.
  • http://ww2.justanswer.com/uploads/MI/MikeG2010/2012-6-7_192640_IMG01612.64x64.jpg Mike G.'s Avatar

    Mike G.

    Master Electrician

    Satisfied Customers:

    5318
    Proven Professional 45 years Experience
  • http://ww2.justanswer.com/uploads/AS/AssuredElectrical/2011-9-13_221243_me.64x64.gif AssuredElectrical's Avatar

    AssuredElectrical

    Master Electrician

    Satisfied Customers:

    2149
    Contractor-40 Years in the ElectricalTrade
  • http://ww2.justanswer.com/uploads/electrifier/2008-12-16_200429_headbob1.jpg electrifier's Avatar

    electrifier

    Master Electrician

    Satisfied Customers:

    1454
    Electrical contractor and electrical inspector for over 24 years with phone and networking expertise
  • http://ww2.justanswer.com/uploads/rich03dungo/2010-3-17_101556_tshirt2.jpg Rich's Avatar

    Rich

    Master Electrician

    Satisfied Customers:

    1115
    Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain
  • http://ww2.justanswer.com/uploads/UR/urelectrician/2012-9-28_223652_JustAnswerPic.64x64.jpg Kevin's Avatar

    Kevin

    Licensed Electrician

    Satisfied Customers:

    993
    27 years as a Licensed Electrical Contractor in Illinois, 5 year college Electrical Instructor, Former Electrical Inspector, Diploma in Digital Electronics, Former Illinois Licensed Home Inspector
 
 
 

Related Electrical Questions

Chat Now With An Electrician
electrifier
electrifier
Owner - Contractor
1455 Satisfied Customers
Electrical contractor and electrical inspector for over 24 years with phone and networking expertise