Ask electrifier Your Own Question
electrifier, Master Electrician
Category: Electrical
Satisfied Customers: 1633
Experience:  Electrical contractor and electrical inspector for over 24 years with phone and networking expertise
Type Your Electrical Question Here...
electrifier is online now
A new question is answered every 9 seconds

how many 12/2 cables can be run in a condit

This answer was rated:

how many 12/2 cables can be run in a condit

electrifier :

12/2 NM cable is considered a round conductor with the major diameter of the cable, the width, used as the diameter of a round cable when figuring conduit fill. Depending on the size of the conduit, 1/2" EMT would allow a single 12/2 NM cable. 3/4" EMT would allow maybe 2 without actually doing the math. Put a box at the end of the conduit and use individual THHN conductors in the conduit to get more circuits. Then it is the normal rules for conduit fill and multiple current carrying conductors. If you want the exact detail please provide the conduit size and confirmation that you are speaking of 12/2 w/G NM cable.

electrifier and other Electrical Specialists are ready to help you