I am installing an eaton 100 amp main breaker panel as an indoor

Resolved Question:

I am installing an eaton 100 amp main breaker panel as an indoor sub panel. I have power to the main breaker but it is not energizing the rest of the panel. Should I be using a main lug instead?
Submitted: 1 year ago.
Category: Electrical
Expert:  Steve G. replied 1 year ago.

Hello there and welcome to Just Answer. My name is XXXXX XXXXX I will be assisting you today. I am an engineer with over 30 years of electrical and electronic training, repair and installation experience. I will try and answer your question accurately and precisely so that we can get you on your way.

Ok, so you have a sub panel with a 100A main breaker. Assuming that this is a residential application, you will have two hot conductors and a neutral (disregard ground for now).

At the top of the breaker (the hot side), what is the voltage between each hot and the neutral? I need two numbers.

Please let me know so that we can continue.

Regards

Steve

Customer: replied 1 year ago.

I am driving to the location i will let you know in a couple of minutes


 

Expert:  Steve G. replied 1 year ago.
Ok, I'll be here.
Customer: replied 1 year ago.

 


 


 


12.08 hot


7.24 on nuetral


 

Expert:  Steve G. replied 1 year ago.

That's on the hot side - on the incoming conductors to the breaker?

You should have 120V both from L1 to N and from L2 to N.

Can you describe what you did at your main panel? I assume that you have a 100A 2 pole breaker feeding the main breaker in your new panel?

I also assume that you pulled over two hots, a neutral and a ground? You terminated the two hots into the top of the main breaker, the neutral to the neutral bar and the ground to the ground bar?

By the way, you need to remove the bonding screw or strap between the neutral and ground bars in that sub panel.

Please let me know so that we can continue.

Regards

Steve

Customer: replied 1 year ago.

I just removed the bonding screw, iam repacing an old screw in type panel with the orange and blue fuses, the 2 hots neutral and ground are connected as you directed.i have 115v on one hot and 115v on the othrer


 

Expert:  Steve G. replied 1 year ago.

Ok, then that sounds right.

When you are confident that everything is correct, turn on the new main breaker and your panel should be energized.

I'll be here if you need further help with this issue. Please let me know.

Regards

Steve

Customer: replied 1 year ago.

the ground (very thick aluminum looking) does not reach the ground bar. I screwed it to the box itself. The top hot wire is red the other is black. Both are connected to the main breaker in the sub-panel.

Expert:  Steve G. replied 1 year ago.

Ok, and between the two (black and red) you should have 240V or thereabouts.

Do you?

If so, turn on the breaker and the sub panel should be energized.

Steve

Customer: replied 1 year ago.

i get 242v on the black and red combined, i can jump fron the hot on the breaker to another breaker and it works. the main breaker is not sending energy to the rest unless i jump it.


 


Is it possable that the new panel box is just bad? I replaced the 100 amp breaker that came installed in the panel with a new one, no bondidng screw is in use

Expert:  Steve G. replied 1 year ago.

Is the breaker 'on'?

Can you try the switch in both positions please?

Customer: replied 1 year ago.

Yes I have turned the 100 amp breaker in on and off positions. the outside main is on and sending power to the main breaker inside but it is not sending juice to the rest of the panel.

Expert:  Steve G. replied 1 year ago.

That's odd.

So there is no voltage on the copper bussing of that panel, but the breaker is connected to it on its load side? And you have the breaker on and you have 240V on the Line side of the breaker?

Customer: replied 1 year ago.

there is a copper strip on the outside panel with the ground bar, however I do not see any copper strip in this eaton panel inside the house

Expert:  Steve G. replied 1 year ago.

The branch circuit breakers mount to the copper bus. It may be tinned so that it looks silver but it is copper. The main breaker has your feeders in one side and the other side likely stabs on to that bus.

How about a photo of that sub panel with the breaker attached? You can upload it here using the paper clip icon or you can email it to experts@pearl.com attn: Steve555

Then I can see what's going on here.

Customer: replied 1 year ago.

i emaile the pictures...the panel is being installed up side down du to not having enough existing wire that ran to the bussman type screw in fuses


 

Expert:  Steve G. replied 1 year ago.

Ok, when I receive the photo from my admin, I will reply back to you.

This may take an hour or more as it is Sunday.

Customer: replied 1 year ago.

I'm getting access denied but here's the links to the photos


 


http://s3.amazonaws.com/f01.justanswer.com/JACUSTOMERcqb2qzp0/2013-06-30_165236_panel3.jpg


 


http://s3.amazonaws.com/f01.justanswer.com/JACUSTOMERcqb2qzp0/2013-06-30_165315_panel.jpg


 


http://s3.amazonaws.com/f01.justanswer.com/JACUSTOMERcqb2qzp0/2013-06-30_165400_panel2.jpg

Expert:  Steve G. replied 1 year ago.

Ok, disconnect the 100A breaker and remove it from the panel. Obviously, you will need to kill the upstream breaker to make it safe.

Get your meter and set it to ohms.

On the back of the breaker are the two 'stabs' that connect the breaker to the panels busbars, one for each 'half' of the breaker. I want you to click the breaker on and then measure the resistance between the screw of each phase and the corresponding bus stab. With the breaker handle in the on position, you should get close to zero ohms for each half of the breaker.

Can you try that please and let me know.

Customer: replied 1 year ago.

We have totally remove this main panel breaker and are returning it to the store. Should we get a main lug panel instead for easier installation? What brand would you recommend.

Expert:  Steve G. replied 1 year ago.

Square D/Eaton is fine. Cutler Hammer, GE, Westingouse etc.

I think maybe the breaker was bad.

I like to have a main breaker on any panel. Have the store test the main breaker for you.

Steve

Steve G., Electrical Engineer
Category: Electrical
Satisfied Customers: 17130
Experience: 27 years in Electrical Engineering, designing electrical plans and specifications.
Steve G. and 3 other Electrical Specialists are ready to help you

JustAnswer in the News:

 
 
 
Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.
 
 
 

What Customers are Saying:

 
 
 
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
< Last | Next >
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
  • Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help. Mary C. Freshfield, Liverpool, UK
  • This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!! Alex Los Angeles, CA
  • Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult. GP Hesperia, CA
  • I couldn't be more satisfied! This is the site I will always come to when I need a second opinion. Justin Kernersville, NC
  • Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around. Esther Woodstock, NY
  • Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know. Robin Elkton, Maryland
 
 
 

Meet The Experts:

 
 
 
  • Mike

    Master Electrician

    Satisfied Customers:

    1425
    Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer
< Last | Next >
  • http://ww2.justanswer.com/uploads/mikepettinato/2009-9-4_41145_DSC005132.jpg Mike's Avatar

    Mike

    Master Electrician

    Satisfied Customers:

    1425
    Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer
  • http://ww2.justanswer.com/uploads/WI/WireitUp/2012-6-17_18212_Photo00006.64x64.jpg Jason's Avatar

    Jason

    Service Technician

    Satisfied Customers:

    3278
    Over 15 years of experience in all types of installations, troubleshooting, and repairs.
  • http://ww2.justanswer.com/uploads/MI/MikeG2010/2012-6-7_192640_IMG01612.64x64.jpg Mike G.'s Avatar

    Mike G.

    Master Electrician

    Satisfied Customers:

    5318
    Proven Professional 45 years Experience
  • http://ww2.justanswer.com/uploads/AS/AssuredElectrical/2011-9-13_221243_me.64x64.gif AssuredElectrical's Avatar

    AssuredElectrical

    Master Electrician

    Satisfied Customers:

    2149
    Contractor-40 Years in the ElectricalTrade
  • http://ww2.justanswer.com/uploads/electrifier/2008-12-16_200429_headbob1.jpg electrifier's Avatar

    electrifier

    Master Electrician

    Satisfied Customers:

    1454
    Electrical contractor and electrical inspector for over 24 years with phone and networking expertise
  • http://ww2.justanswer.com/uploads/rich03dungo/2010-3-17_101556_tshirt2.jpg Rich's Avatar

    Rich

    Master Electrician

    Satisfied Customers:

    1115
    Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain
  • http://ww2.justanswer.com/uploads/UR/urelectrician/2012-9-28_223652_JustAnswerPic.64x64.jpg Kevin's Avatar

    Kevin

    Licensed Electrician

    Satisfied Customers:

    993
    27 years as a Licensed Electrical Contractor in Illinois, 5 year college Electrical Instructor, Former Electrical Inspector, Diploma in Digital Electronics, Former Illinois Licensed Home Inspector
 
 
 

Related Electrical Questions

Chat Now With An Electrician
Steve G.
Steve G.
Chief Engineer
330 Satisfied Customers
27 years in Electrical Engineering, designing electrical plans and specifications.