I have an older Bryant residential service panel. The label

Resolved Question:

I have an older Bryant residential service panel. The label is missing, so I can't be sure of the model number. It is the size and configuration of a 200A panel but has a 175A main breaker. How likely is it that the panel is actually rated for 200A?
Submitted: 1 year ago.
Category: Electrical
Expert:  AssuredElectrical replied 1 year ago.

AssuredElectrical :

Welcome. My name is XXXXX XXXXX would be glad to assist.

AssuredElectrical :

Have you removed the cover to see if any labels are on the inside?

AssuredElectrical :

How many positions are available? Counting the available slots for all the breaker positions?

Customer:

The cover has been removed and there are no labels. Give me a minute and I will tally the breaker positions.

AssuredElectrical :

ok

Customer:

There are 22 one inch positions including the main breaker

AssuredElectrical :

So, it is 20 total, 10 on the left and 10 on the right?

Customer:

This service has a single column of breaker with the main near the center of the buss bar

AssuredElectrical :

Ok, sounds like another brand, bryants were normally left and right, but could be an early version I guess

AssuredElectrical :

What breakers are in the panel? Can you read the models?

AssuredElectrical :

Is the main a plug in style?

AssuredElectrical :

or bolted?

Customer:

I should mention that this is a residential all-in-one. All the breakers appear to be original and all - including the main - are Bryant.

AssuredElectrical :

ok

AssuredElectrical :

well that allows 20 circuits which would be very small for a 200, usually that is associated with 150 and smaller.

AssuredElectrical :

The label is what code requires to go by and makes it really difficult to determine

AssuredElectrical :

Is the main bolted to the buss or plug?

Customer:

I am getting a picture of it

AssuredElectrical :

ok, thanks

Customer:

Your system doesn't like my file type. I'll PDF it and send in a minute.

AssuredElectrical :

JPG or GIF?

Customer:

Full Size Image

Customer:

Full Size Image

AssuredElectrical :

give them a min to upload so I can see, they are loading now

Customer:

Full Size Image

AssuredElectrical :

I can see it, the style on the main is a plug style across the whole buss

AssuredElectrical :

You have a few MPT styles in there and a GE also

AssuredElectrical :

all are not Bryant

Customer:

Yes, those that appear to be original are bryant as is the main. The question here is - did bryant produce a service that was rated for 175A max or is this a 200A buss with a 175A main?

AssuredElectrical :

well, without the label it cannot be identified. Judging by the quantity of spaces, I would guess no. Usually the Main always represented the buss size accordingly. Rare to ever have a Main smaller than the buss rating...But then again, it is a guess based on the picture and information. There is no way for anyone to determine exactly the rating.

AssuredElectrical :

Is this for informational pirposes?

Customer:

No, we want to add solar so the actual rating of the buss is important. It is uncommon to see a 175A service panel. usually 100, 125, 200. If Bryant marketed a 175 at all then I should assume that is what I have. If they never produced a service with a 175 max buss, then this is likely to be a 200.

AssuredElectrical :

I did a quick search and found the Bryant 175 amp mains, so it was a common used like the 150 and 200a

AssuredElectrical :

I wish it could be 100% definitive, but Code states, the label must be intact to determine the internal components

AssuredElectrical :

I tried to find one similar and not found one as yet through some of my forums.

Customer:

I known that the breakers you describe were produced. What I don't know is did they produce a service with a 175A max buss. There should be a model number somewhere that lists that as a specification and, perhaps, a picture that matches what I have.

AssuredElectrical :

I understand, the model number unfortunately is on the labels along with all the ratings, breakers allowed etc. I see this many times and it is difficult to do some work because of the situation for customers.

AssuredElectrical :

The internals were never labeled as to parts, that info also is on the labels. Always a catch 22

AssuredElectrical :

Any electrical contractor would have to use what is there for the basis, the 175A main. Otherwise they would be against code and it would fail inspections because of no documentation to show otherwise.

Customer:

Is there a list of residential all in ones marketed by bryant that lists the product numbers and specs. If they did not market a service with 175 max that would be an indicator.

AssuredElectrical :

Bryant went out of business years ago. Cutler Hammer purchased the branding and supply the BR style breakers that fit the panels.

AssuredElectrical :

There may be something hidden in their files somewhere, but again, if you have no label there is not a way to compare. The 150 looks like the 200 on all panels, it is the buss makeup and design that rates the panels.

AssuredElectrical :

I put out a notice on a forum we use to communicate with electrical experts across the country, maybe I will get a hit

Customer:

Did Bryant have some convention in the way they designated the model numbers? If I can determine that, I can search on the model number that would correspond to a 175A mode.

AssuredElectrical :

I do not know how all the older styles were designated. I can opt out if you wish and pass this to any expert who may have knowledge of such. Do not know how long it would take or if anyone would could have the information.

AssuredElectrical :

When a company goes out of business the files are pretty much internal to the company that bought them.

Customer:

This is why I was willing to spend 30 bucks to research this. Are we at a dead end?

AssuredElectrical :

I cannot provide anymore, sorry. Code is strict that a label must be present for evaluation.

AssuredElectrical :

I can opt out, and see if anyone picks up the question.

AssuredElectrical :

They will email you if someone posts

Customer:

All right. Thanks anyway.

AssuredElectrical :

Costs nothing here, just no rating and see if another expert can assist.

AssuredElectrical :

Is that what you want to do?

Customer:

If they is a way to get something more definitive, I will try it but we seem to be out of avenues to explore. Is that your take as well?

AssuredElectrical :

To be honest, yes because of how the code ties our hands for evaluation and installing electrical equipment. We cannot add a breaker without knowing the label contents to be sure a breaker is designed for the panel with a couple exceptions on the new owners of the old company.

AssuredElectrical :

If I told you yes it is rated 200, I have nothing to substantiate it, and that is liability. Prefer always to know 100% before advising, as we all do in this case

AssuredElectrical :

Ho bad is it deterring you if it is rated at 175 with the solar?

AssuredElectrical :

Your load looks very minimal with the amount of circuits.

Customer:

I understand. I did not expect to define the service on this forum - just get information on how proceed with the determination. We need all the capacity we can get on the existing service. Changing the service is not an option due to cost.

AssuredElectrical :

I understand. Possibly a call to Cutler Hammer is an option. Sometimes you can get through to an engineer willing to assist on such matters.

AssuredElectrical :

Not a guarantee. Cutler hammer bought them out when they went under

AssuredElectrical :

Eaton Corporation that is now

Customer:

Okay, I guess I'll try something with them.

AssuredElectrical :

CLICK HERE

AssuredElectrical :

Customer support option is where I would start

AssuredElectrical :

Will take some time, I have have had several days go by before getting anything with todays equipment.

Customer:

OK, thanks. How do we terminate?

AssuredElectrical :

If you are satisfied with my assistance you can rate my service, otherwise we can just end it here and be done.

Customer:

Thanks for your help. I'll pay for effort.

AssuredElectrical :

Ok, it is appreciate. Thank you. If something does pop up, I can post to you even after this is closed out

AssuredElectrical, Master Electrician
Category: Electrical
Satisfied Customers: 3218
Experience: Contractor-40 Years in the ElectricalTrade
AssuredElectrical and 4 other Electrical Specialists are ready to help you

JustAnswer in the News:

 
 
 
Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.
 
 
 

What Customers are Saying:

 
 
 
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
< Last | Next >
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
  • Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help. Mary C. Freshfield, Liverpool, UK
  • This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!! Alex Los Angeles, CA
  • Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult. GP Hesperia, CA
  • I couldn't be more satisfied! This is the site I will always come to when I need a second opinion. Justin Kernersville, NC
  • Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around. Esther Woodstock, NY
  • Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know. Robin Elkton, Maryland
 
 
 

Meet The Experts:

 
 
 
  • Mike

    Master Electrician

    Satisfied Customers:

    1425
    Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer
< Last | Next >
  • http://ww2.justanswer.com/uploads/mikepettinato/2009-9-4_41145_DSC005132.jpg Mike's Avatar

    Mike

    Master Electrician

    Satisfied Customers:

    1425
    Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer
  • http://ww2.justanswer.com/uploads/WI/WireitUp/2012-6-17_18212_Photo00006.64x64.jpg Jason's Avatar

    Jason

    Service Technician

    Satisfied Customers:

    3278
    Over 15 years of experience in all types of installations, troubleshooting, and repairs.
  • http://ww2.justanswer.com/uploads/MI/MikeG2010/2012-6-7_192640_IMG01612.64x64.jpg Mike G.'s Avatar

    Mike G.

    Master Electrician

    Satisfied Customers:

    5318
    Proven Professional 45 years Experience
  • http://ww2.justanswer.com/uploads/AS/AssuredElectrical/2011-9-13_221243_me.64x64.gif AssuredElectrical's Avatar

    AssuredElectrical

    Master Electrician

    Satisfied Customers:

    2149
    Contractor-40 Years in the ElectricalTrade
  • http://ww2.justanswer.com/uploads/electrifier/2008-12-16_200429_headbob1.jpg electrifier's Avatar

    electrifier

    Master Electrician

    Satisfied Customers:

    1454
    Electrical contractor and electrical inspector for over 24 years with phone and networking expertise
  • http://ww2.justanswer.com/uploads/rich03dungo/2010-3-17_101556_tshirt2.jpg Rich's Avatar

    Rich

    Master Electrician

    Satisfied Customers:

    1115
    Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain
  • http://ww2.justanswer.com/uploads/UR/urelectrician/2012-9-28_223652_JustAnswerPic.64x64.jpg Kevin's Avatar

    Kevin

    Licensed Electrician

    Satisfied Customers:

    993
    27 years as a Licensed Electrical Contractor in Illinois, 5 year college Electrical Instructor, Former Electrical Inspector, Diploma in Digital Electronics, Former Illinois Licensed Home Inspector
 
 
 

Related Electrical Questions