In the NEC book page 70-168 paragraph 314.16 (b) (1) conductor

 
AssuredElectrical's Avatar
  • Answered by:AssuredElectrical
  • Master Electrician
  • Positive Feedback: 98.5 %
  • Accepted Answers: 1613
Verified Expert
in Electrical

Recent Feedback

Positive
What a find! Needing help with a breaker that kept tripping, I was connected to...
Positive
Excellent service! Gave me just what I needed! Thanks!
Positive
Satisfait du travail de l'expert. Très compétent. Merci!
Positive
Assured Electrical tried to help me with the problem I am having with my pool...
Positive
great help. pertinent answers to question.
Positive
excellent help.
Positive
Extremely helpful and professional!
Positive
Great Help, Thanks for explaining and telling where to get what I needed.
Positive
He was fantastic. So helpful and we LEARNED how to put in these 3 way switches....
Positive
Great. Provided diagrams too.

Customer Question

In the NEC book page 70-168 paragraph 314.16 (b) (1) conductor fill, it seems that the first line of the paragraph contradicts the last sentence. Can you explain this in lay-mans terms. It sounds like you deduct the conductors that are terminated on the device, therefore donot count these conductors at all.
Thankyou, Confused!

Submitted: 403 days and 15 hours ago.
Category: Electrical
Value: $9
Status: CLOSED

Accepted Answer

Picture
Expert:  AssuredElectrical replied403 days and 15 hours ago.


AssuredElectrical :

Hi, Welcome to Just Answer. My name is XXXXX XXX would be glad to assist.

AssuredElectrical :

It means that if a conductor enters the box and doesnt connect to another wire, looped or connect to a device, dont count it

AssuredElectrical :

Basically, it is not used for anything.

Customer :
AssuredElectrical :

Sorry, mis read your post

AssuredElectrical :

What that is stating, is like you have a pigtail on the wires. Connect the whites together and pigtail to a receptacle for instance

AssuredElectrical :

That pigtail neither enters or leaves the box

AssuredElectrical :

it is just inside the box

AssuredElectrical :

Not considered a conductor for fill requirements.

AssuredElectrical :

Sorry for any confusion

AssuredElectrical :

The system says you have posted, but I do not see anything.

Customer :

Sorry 1st time using this. just checked my email found answer was waiting on just answer didnot see any reply. In my class study book it has a picture of two conductors coming into a box and the white and black are both under a screw on a device. But the statement below the picture says; Each conductor originating outside the box and terminating inside the box is rated as one conductor. Two are shown here: therefore a deduction of two conductors must be made. This is from NCCER Level One Corriculum.

Customer :

Also, to 100% answer my question, when conductors terminate on a screw to a device or wire to a light fixture, they are not considered dead-ends and you do not deduct them back out!

AssuredElectrical :

Ok, you stated:In my class study book it has a picture of two conductors coming into a box and the white and black are both under a screw on a device. But the statement below the picture says; Each conductor originating outside the box and terminating inside the box is rated as one conductor.

AssuredElectrical :

Yes, each conductor is counted. The picture and statement are the same thing. Each one enters and is used and terminated.

Customer :

But it also says below that sentence, Two are shown here; therefore two conductors must be deducted.

AssuredElectrical :

Each single wire is a conductor. So each one counts towards the total.

AssuredElectrical :

A conductor is not a cable.

Customer :

Ok! so basically what that statement means is that when it says deducted it means for the purpose of the box fill calculations to give total.

AssuredElectrical :

Yes, you add up the total of the conductors and subtract them from the cu/in of the box capacity

AssuredElectrical :

That is why the say deduct from the total of the box cu/in. It is a little misleading

AssuredElectrical :

Receptacle box has 2 cables 14/2 enter a box and terminate----Each black is 2, each white is 2 and both grounds together are 2 The receptacle is 4. Total is 14 cu/in. Deduct that from the box capacity of 18 and you have 4 cu/in leftover.

AssuredElectrical :

So, that is accepted

AssuredElectrical :

If the box is 12 cu/in, it would fail

Customer :

I understand, thankyou very much! I have another small question may i ask it?

AssuredElectrical :

Sure go for it

Customer :

If you run a 12/2 wire on a 20 amp breaker, and use a 15amp switch can you use a 14/2 wire for the light leg?

AssuredElectrical :

NO

AssuredElectrical :

The switch can carry 20 amps on the feed through rating so it is allowed. The 14 wire is not rated for 20 amps

AssuredElectrical :

Read the switch ratings and it will say 20 amps through put, just like a 15 amp receptacle

Customer :

Soif you use 12/2 wire you can't or only because you used a20amp breaker instead of a 15 amp breaker?

AssuredElectrical :

once the 12/2 leaves the panel, everything on that circuit MUST be #12 or larger

AssuredElectrical :

doesnt matter what breaker is used 15 or 20

AssuredElectrical :

It is the wire. Someone in the future may see the 12 and put a 20 amp breaker. Then the 14 burns the house down. They had no idea that someone used a 15 for a special connection

Customer :

I see. Thankyou very much for your assistance, it's been very enlighting!

AssuredElectrical :

You are very welcome. Glad to be of service. If your are satisfied with my
assistance to your questions then, please do click the Accept for my time.

Expert TypeMaster Electrician
Category: Electrical
Pos. Feedback: 98.5 %
Accepts: 1613
Answered: 5/12/2012

Experience: Contractor-40 Years in the ElectricalTrade

Ask this Expert a Question >
 
Tweet

Electricians are Online Right Now

Ask Your Question Now
Electrical Questions Date Submitted
We have a washer/dryer laundry unit all in one. The electrical 6/14/2013
I bought a programmable light switch with the following: black-power white-neutral BLUE 6/13/2013
I have a Square D breaker panel, and I need to add a 2 phase, 6/13/2013
I have a cargo trailer that has an progressive dynamics intelli 6/12/2013
My Electrician installed by Vercelli fan yesterday but there 6/12/2013
Hi ....I am having problems with my electrical...my 60 amp 6/11/2013
I have a light switch with three black wires and three white 6/10/2013
The underground wire that comes from my house panel to my workshop 6/9/2013
Hello I have a 240v outlet and want to add a 120v outlet nearby. 6/7/2013
I have an exterior decorative light column 5 feet tall with 6/7/2013
RSS
Next 10 >
Ask an Electrician
Type Your Electrical Question Here...
characters left:

Top Electrical Experts

See More Electricians

In The News

Nbc
Washington Post
New York Times
Cnn
Learn More

How It Works

  • Ask an Expert
  • Get a Professional Answer
  • Ask Followup Questions
  • 100% Satisfaction Guarantee
Learn More
 
 
 

Recent Articles in Electrical

  • Electric Pull Switch Related Questions
  • Questions about OHMS
  • Questions on Light Switch Problems
  • Electrical Transfer Switch Questions
  • Questions on Electrical Plugs
  • Questions on Generator Troubleshooting
  • Questions on Electrical Bus Bar
  • Questions on Electrical Timer Switches
  • Questions on Thermostat Problems
  • Questions on Voltage Problems
All Electrical Articles
 
 
 

Ask an Electrician

Get a Professional Answer. 100% Satisfaction Guaranteed.
80 Electricians are Online Now
Type Your Electrical Question Here...
characters left:
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.
Truste
Contact Us | Terms of Service | Privacy & Security | About Us | Our Network
© 2003-2013 JustAnswer LLC
  • Pearl.com
  • JustAnswer UK
  • JustAnswer Germany
  • JustAnswer Spanish
  • JustAnswer Japan