what size of electrical wire do I need for an 800 amp single

Resolved Question:

what size of electrical wire do I need for an 800 amp single phase underground service that will be 350 feet from the transformer.
Submitted: 3 years ago.
Category: Electrical
Expert:  AssuredElectrical replied 3 years ago.

AssuredElectrical :

Hi, Welcome to Just Answer. My name is XXXXX XXXXX would be glad to assist.

AssuredElectrical :

800 amp , single phase, 350 feet. Will this be in conduits or buried directly?

Customer:

I'm not sure which route I want to go so am interested in an answer for both options

AssuredElectrical :

You have several options. There will be parallel runs.

AssuredElectrical :

Aluminum?

Customer:

yes

Customer:

im not sure what you mean by parallel runs

AssuredElectrical :

3 sets 400 mcm in conduit is an option 270 amp per set

AssuredElectrical :

What transformer is this? Power company?

Customer:

we live in rural district and is a setting for grain facility/general farm operation

AssuredElectrical :

You cannot get 800 amps from just 3 cables. Takes multiple sets of 3.

AssuredElectrical :

So, multiple conduits

AssuredElectrical :

I assume you have already verified with the power company that they can accommodate you?

Customer:

so i need 3 runs of conduit with 400 mcm triplex in each one? yes the power company has been notified and says that they have more than enough to accommodate us.

AssuredElectrical :

Tri-plex? Conduit would be single cables. THWN or the like. Triplex would be the underground cable in earth.

AssuredElectrical :

Insulation of the cable is very critical.

AssuredElectrical :

Do you know exactly what it is you have in mind? Manufacturer?

Customer:

What size triplex would i need then if i did want to direct bury it.

Customer:

what do you mean by manufacturer.

AssuredElectrical :

It is all about the insulation class of the manufactured cable

AssuredElectrical :

Here is an example:

AssuredElectrical :

  • Type RHH/RHW-2 rating to UL 44

  • Type USE-2 per UL 44

AssuredElectrical :

With this cable, it would be 3 -350 mcm runs.

Customer:

we are considering URD triplex

AssuredElectrical :

Like here?

AssuredElectrical :

That is the same 3 runs- 350 mcm

Customer:

Yes that is the wire we are considering. so can't i just run 400 mcm triplex and run that through pvc conduit and bury it

AssuredElectrical :

I am trying to understand, the cable is made for direct bury. You want to conduit it too?

Customer:

yes. just for the ease of handling/running it through conduit. and thats what we've always done. is the loss of voltage less if run in conduit or has no effect

AssuredElectrical :

Cables are large, voltage drop is not your issue.

AssuredElectrical :

The key is whether you have to de-rate the cable in conduit.

Customer:

so if i would run 400 mcm triplex in conduit and bury it, this would handle 800 amps single phase 350 feet away? is that correct? and if so what would be the approximate diameter of one of the strands of triplex?

AssuredElectrical :

1 run of 400 mcm triplex will not carry the 800 amps

AssuredElectrical :

I am finding the information, be just a moment. Thanks

AssuredElectrical :

Do you understand on the 400 mcm?

Customer:

3 sets of triplex direct bury or in conduit (whatever I decide) would be sufficient. correct? as far as the 400 mcm I guess i really don't quite understand that -- is that wire size?

AssuredElectrical :

yes, it is wire size

AssuredElectrical :

diameter of the cables

AssuredElectrical :

3 sets will carry the 800 amp

AssuredElectrical :

I am trying just to verify putting underground cable in a conduit. Not common.

AssuredElectrical :

Diameter of 350 in that URD is 1.736" each cable

AssuredElectrical :

When you are going to purchase the cable, the company selling it should know on the conduit question.

Customer:

thanks for answering my questions and your patience

AssuredElectrical :

Your welcome. Been a pleasure. If your are satisfied with my answers , please do
click the Accept for my time. You can come back to this page anytime.

AssuredElectrical, Master Electrician
Category: Electrical
Satisfied Customers: 3152
Experience: Contractor-40 Years in the ElectricalTrade
AssuredElectrical and other Electrical Specialists are ready to help you

JustAnswer in the News:

 
 
 
Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.
 
 
 

What Customers are Saying:

 
 
 
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
< Last | Next >
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
  • Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help. Mary C. Freshfield, Liverpool, UK
  • This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!! Alex Los Angeles, CA
  • Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult. GP Hesperia, CA
  • I couldn't be more satisfied! This is the site I will always come to when I need a second opinion. Justin Kernersville, NC
  • Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around. Esther Woodstock, NY
  • Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know. Robin Elkton, Maryland
 
 
 

Meet The Experts:

 
 
 
  • Mike

    Master Electrician

    Satisfied Customers:

    1425
    Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer
< Last | Next >
  • http://ww2.justanswer.com/uploads/mikepettinato/2009-9-4_41145_DSC005132.jpg Mike's Avatar

    Mike

    Master Electrician

    Satisfied Customers:

    1425
    Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer
  • http://ww2.justanswer.com/uploads/WI/WireitUp/2012-6-17_18212_Photo00006.64x64.jpg Jason's Avatar

    Jason

    Service Technician

    Satisfied Customers:

    3278
    Over 15 years of experience in all types of installations, troubleshooting, and repairs.
  • http://ww2.justanswer.com/uploads/MI/MikeG2010/2012-6-7_192640_IMG01612.64x64.jpg Mike G.'s Avatar

    Mike G.

    Master Electrician

    Satisfied Customers:

    5318
    Proven Professional 45 years Experience
  • http://ww2.justanswer.com/uploads/AS/AssuredElectrical/2011-9-13_221243_me.64x64.gif AssuredElectrical's Avatar

    AssuredElectrical

    Master Electrician

    Satisfied Customers:

    2149
    Contractor-40 Years in the ElectricalTrade
  • http://ww2.justanswer.com/uploads/electrifier/2008-12-16_200429_headbob1.jpg electrifier's Avatar

    electrifier

    Master Electrician

    Satisfied Customers:

    1454
    Electrical contractor and electrical inspector for over 24 years with phone and networking expertise
  • http://ww2.justanswer.com/uploads/rich03dungo/2010-3-17_101556_tshirt2.jpg Rich's Avatar

    Rich

    Master Electrician

    Satisfied Customers:

    1115
    Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain
  • http://ww2.justanswer.com/uploads/UR/urelectrician/2012-9-28_223652_JustAnswerPic.64x64.jpg Kevin's Avatar

    Kevin

    Licensed Electrician

    Satisfied Customers:

    993
    27 years as a Licensed Electrical Contractor in Illinois, 5 year college Electrical Instructor, Former Electrical Inspector, Diploma in Digital Electronics, Former Illinois Licensed Home Inspector
 
 
 

Related Electrical Questions