I want to run 220 to my barn which is about 140 ft away. The main connection is on my house and I will put sub panel in the barn. Do I need to run a 4 wire or 3 wire and what size for 30 amp?
Hi, thanks for posting your question on JustAnswer...
Please let me know when you have joined the chat.
I'm here
Great...You'll need to run four wires total (hot, hot, neutral, ground). You'll need at least #10 conductors. With that, and a balanced 30A load (15A on each leg) you'll be within the recommended 5% Voltage drop range. But, if for example, one leg carries 18A, that leg will exceed the 5% voltage drop recommendation. So, on that basis, I'd recommend #8 conductors.
A couple of other notes you may not have considered:
1) Make sure your neutral and ground bars are separated in the sub-Panel (you usually have to purchase a ground bar kit as they don't typically come with sub-panels)2) Make sure you drive two ground rods (at least 6' apart)outside the building and bond them to the ground bar in the panel with one continuous ground wire3) Make sure your sub-panel is located nearest the point of entrance of the feeder cables. In other words, the feeder cables can't come into the building, travel through the building to the other side, then to the sub-panel.
(on that last note, the sub-panel needs to be be either a)outside the building or b)inside nearest the point of entrance of those feeder cables)
Understand: Would you recommend useing direct burial cable or should I put this in Conduit?
Personally, I always always use conduit. It's not much more $$, and it provides for a more flexible, reliable installation.
(conduit with THHN conductors, that is)
Thanks for the help?
Not a problem. Glad to help. Happy New Year's, and take care!
I'm sorry one more question. should the wire be copper or aluminun?
Copper
Thanks again and Happy New Year. I'm done.
Thank you!
Experience: Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer
Please don't forget to click Accept so I'm credited for answering your question, if you're happy with my service and you feel I've adequately answered your question. Some customers don't realize that you they have to click Accept to close the question and credit me for answering it; again, this is only if you're happy with my service (this is a satisfaction based service). Thanks!