Recent Feedback
i have a ge powervent water heater model number GG40T06PVK . it is in lock out. how do i reset it. i know there is a button combonation you press but i don't remember it.
Optional Information: Make: ge Model: GG40T06PVK Already Tried: power on and off.
http://products.geappliances.com/MarketingObjectRetrieval/Dispatcher?RequestType=PDF&Name=AP13787 GE US Power Vent.pdf
This is a link to the complete use and care manual. You have a gas water heater. Not sure what you mean by "lock out" If you mean you need to light the pilot detailed instructions inside the manual. No electronics on this one to be locked out so if the manual isn't a help please post a more detailed question as to what you need. Thanks!
Also please remember to click accept and leave feedback so I get credit for the question. You can still communicate after you do this. Thanks again!
Brandon
Experience: 7 years Repairing Appliances, Factory Trained in Several Major Brands
it does have electronics on it and no pilot light. it';s self lighting.....i.e. glow plug. the lockout is do to flammable vapor sensor and the only place it says so is on the heater itself...i read the manual....i had to call ge befor and they told me a button combo to press to reset it.....but i don't remember it. there is only 2 buttons on it.
Flammable Vapors Sensed (FVS) Reset Procedure
After a flammable vapor lockout has been initiated, a manual reset must be performed to restore
operation. The following should be done by a qualified service person after the hazard has been
removed:
1 Manual reset is accomplished by first, turning off power to the water heater for 10
seconds.
2 Restore the power to the water heater.
3 Within 10 seconds of restoring power, press the two temperature adjust buttons
simultaneously until the left (green) "Vacation" LED begins to blink (approx. 5 second
delay). Once the Vacation LED begins to blink, release both buttons.
4 Again, within 10 seconds, press both temperature adjust buttons simultaneously until the
Vacation LED is on steady (approx. 5 second delay).
5 Release the two buttons, the microcomputer will clear the FVS lock-out and normal
operation will then be restored.
still both lights are on......what now.
I would say if you have tried to reset it and the lights are still there, the sensor is actually detecting flammable vapor. Do you have anything nearby like gas, or ammonia, or anything that might be confusing the sensor? If not and the reset isn't working you may have a bad sensor.
Below is the sensor test procedure to rule that out
The self diagnostic test has
detected the presence of
flammable vapors.
The Intelli-Vent control is
programed to lock-out and
display this error code if the
resistance value it senses from
the FV sensor is above 70,000
ohms but remains below
1,700,000 ohms.
The Intelli-Vent control is in a
hard lock-out condition that
cannot be reset by cycling power
to the water heater. See the
instructions below for the reset
procedure.
1 Turn off power to the water heater. Carefully check
the surrounding area for any substances such as
gasoline, paint, paint thinners, or cleaners that could
emit flammable vapors. Remove anything that can
potentially emit flammable vapors from the area and
store it properly in a different location.
2 Ensure power to the water heater is turned off.
Remove the FV sensor from it's bracket on the base
ring of the water heater and disconnect both wires to
the sensor. Take a resistance reading between the
two wiring terminals of the FV sensor and note the
resistance values.
Perform this test once in the area by the water heater
and a second time outdoors after allowing the sensor
to acclimate to the outdoor atmosphere for 5
minutes.
Service Note: These resistance readings should be
taken using an ohm scale above70,000 ohms.
3 If the resistance of the FV sensor is above 70,000
ohms during the indoor test only and the resistance
reading taken in the outdoor atmosphere dropped
below 70,000 ohms. Re-check the area surrounding
the water heater for substances that could be
emitting flammable vapors. Remove any such
substances from the area and store them properly in
a different location. Repeat step 2.
4 If the resistance of the FV sensor is above 70,000
ohms during the indoor and outdoor tests - replace
the flammable vapor sensor.
5 If the resistance of the FV sensor was below 70,000
ohms during the indoor and outdoor tests and all the
steps above have been performed - replace the
Intelli-VentTM control.